  1. Replies
    65$$
    Views
    1,445

    Yes, but this section says the EGC never has to...

    Yes, but this section says the EGC never has to be larger than the circuit conductors, regardless of what table 250.122 says.

    I am not sure what you mean by "not directly connected". You still...
  2. here is some debugging info from AB. ...

    here is some debugging info from AB.

    http://www.ab.com/support/abdrives/22comm/22comme/led.html

    if you have a keypad or him you can reset the card to the default parameters.
  3. I looked it up. It is a 22-comm-e. A couple...

    I looked it up. It is a 22-comm-e.

    A couple things to try.

    I have noticed that some of the AB Ethernet products don't send out their MAC ID for the BootP server to find except when the card...
  4. Replies
    65$$
    Views
    1,445

    What does it tell you about minimum size here? ...

    What does it tell you about minimum size here?

    Sent from my SM-G900R4 using Tapatalk
  5. Powerflex 40 drives don't come with an Ethernet...

    Powerflex 40 drives don't come with an Ethernet card. It is a separate card you have to add. There is an RJ45 port on powerflex 40 drives but it is not ethernet. I forget what the part number is....
  6. why did they put it in and why are they now...

    why did they put it in and why are they now taking it out?

    it seems to me that there has always been a requirement to account for higher than normal ambient temperatures even though it seems to be...
  7. most big breakers you are supposed to do some...

    most big breakers you are supposed to do some kind of testing on now and then. if they are kept in a clean area, you can probably get by with not doing much of anything for the life of the product. I...
  8. Modern circuit breakers are every bit as reliable...

    Modern circuit breakers are every bit as reliable as fuses and disconnect switches if they are properly maintained. In general, they are also more cost-effective above about 200 amps most of the time...
  9. Replies
    14$$
    Views
    325

    Might be more cost effective to just move the...

    Might be more cost effective to just move the Transformer.
  10. Replies
    15$$
    Views
    408

    In general it is possible, especially for smaller...

    In general it is possible, especially for smaller Motors. Like many things there are certain limitations but it's not an uncommon thing to do. It might be almost is cost effective to get two small...
  11. Replies
    65$$
    Views
    1,445

    take a look at 250.122 (A).

    take a look at 250.122 (A).
  12. Replies
    65$$
    Views
    1,445

    i agree the sections stand alone. However...

    i agree the sections stand alone.

    However your first assertion is not quite there. neither section exempts you from running an EGC with the other conductors which is found in another section. It...
  13. Replies
    2$$
    Views
    146

    not part of the code. design decision. ask the...

    not part of the code. design decision. ask the engineer.
  14. Replies
    7$$
    Views
    270

    We had a really disgusting cabinet came in for...

    We had a really disgusting cabinet came in for rebuilding once. We rented a pressure washer and used simple green as a detergent to wash all the components and the cabinet with. Only one power supply...
  15. Replies
    4$$
    Views
    251

    I don't know what outdoor type Romex is. I don't...

    I don't know what outdoor type Romex is. I don't recall there is such a thing.

    the conductors have to have an ampacity exceeding the calculated load. What is the calculated load?

    I don't...
  16. Replies
    4$$
    Views
    170

    yes. what you have missed is that the prints...

    yes. what you have missed is that the prints asked for it and that is what you presumably contractually agreed to do when you accepted the P.O. Just because something is not required by code does not...
  17. Replies
    22$$
    Views
    549

    Is it even listed to begin with? Does the code...

    Is it even listed to begin with?

    Does the code require it be listed?

    Does the code even apply to this piece of equipment?

    In any case, you can't "remove the listing" via a modification. It...
  18. Replies
    17$$
    Views
    644

    I am 5'11" tall. I don't consider myself short so...

    I am 5'11" tall. I don't consider myself short so no estimate from me. :)

    700 SF is a small house. a lot of places it is skirting the minimum SF required.
  19. Replies
    65$$
    Views
    1,445

    IMO, the system grounding here refers to...

    IMO, the system grounding here refers to connecting the electrical system to earth (i.e.-creating a grounded conductor), not whether you have to route an EGC with the circuit conductors.
  20. Replies
    5$$
    Views
    254

    why would you need it anyway? the transformer pad...

    why would you need it anyway? the transformer pad is a structure that needs its own GES. There would need to be either an EGC or a supply side bonding jumper going back to the service depending on...
  21. Replies
    80$$
    Views
    1,701

    It does seem pretty clear.

    It does seem pretty clear.
  22. Replies
    5$$
    Views
    202

    it seems to me that once you have a PV system...

    it seems to me that once you have a PV system like this it triggers the requirements of 690.47 to have a grounding electrode system, while a standalone PV light is not a system.
  23. Replies
    5$$
    Views
    254

    effective at what? for the most part it does not...

    effective at what? for the most part it does not serve any purpose at all.
  24. Replies
    5$$
    Views
    348

    One could certainly learn to bake bread in much...

    One could certainly learn to bake bread in much less than a day. Most people could learn it from a ten minute youtube video, at least enough to make a simple bread.

    I don't think the question is...
  25. I doubt the lugs are only rated at 100A if they...

    I doubt the lugs are only rated at 100A if they accept wire as large as 350 kcm. I seem to recall the connector standard requires that they be able to take the full ampacity of whatever wire is...