The solution may be as simple as using 600 V...
The solution may be as simple as using 600 V sheilded tray cable.
But first look at the VFD and find out what type of circuit the wiring to the motor stat is. What you are looking for is "Class 1"...
|
Forum: NEC
11-17-2009, 06:51 PM
|
|
Replies: 34
Views: 654
|
Forum: Lighting
11-17-2009, 04:58 PM
|
|
Replies: 4
Views: 138
|
Forum: NEC
11-16-2009, 04:33 PM
|
|
Replies: 14
Views: 271
|
Forum: Exam Preparation
11-16-2009, 03:29 PM
|
|
Replies: 7
Views: 214
In Washington you can take any trademarked book...
In Washington you can take any trademarked book into the test.
The test is open book, but the idea is to test you on subjects you have not dealt with before, to see if you can find the information. ...
|
Forum: NEC
11-16-2009, 03:23 PM
|
|
Replies: 4
Views: 145
|
Forum: Grounding versus Bonding
11-13-2009, 12:23 PM
|
|
Replies: 4
Views: 213
|
Forum: Grounding versus Bonding
11-13-2009, 12:11 PM
|
|
Replies: 18
Views: 462
|
Forum: Lighting
11-12-2009, 02:05 PM
|
|
Replies: 13
Views: 403
I had a Wellworth fixture, 1.6 gpm flush, but I...
I had a Wellworth fixture, 1.6 gpm flush, but I replaced it with a dual flush toilet, its worked really well. I got it at Costco of all places to buy a fixture.
For a luminaire, I just looked at a...
|
Forum: Continuing Education (CEU)
11-12-2009, 02:02 PM
|
|
Replies: 7
Views: 183
|
Forum: Low Voltage and Limited Energy
11-12-2009, 11:59 AM
|
|
Replies: 21
Views: 768
Article 820 , although the title is misleading....
Article 820 , although the title is misleading. Where the coax enters the building, install an impulse supressor, transistion to the interior listed coax. With the inpulse supressor create a single...
|
Forum: NEC
11-12-2009, 11:14 AM
|
|
Replies: 10
Views: 416
|
Forum: NEC
11-12-2009, 11:12 AM
|
|
Replies: 3
Views: 82
|
Forum: NEC
11-12-2009, 11:03 AM
|
|
Replies: 19
Views: 782
Unused current?
Well, they are selling you...
Unused current?
Well, they are selling you snake oil.
First off, its a violation of the mfg panel listing unless the device is listed by that mgf as an allowed accessory. Thats 110.3(B).
...
|
Forum: Grounding versus Bonding
11-10-2009, 03:34 PM
|
|
Replies: 6
Views: 156
If the neutral is not transfered "solidly...
If the neutral is not transfered "solidly connected" then no ground rods are required.
Electricans and inspectors don't understand this, so they require ground rods. Now the mfgs (Generac for one)...
|
Forum: Grounding versus Bonding
11-10-2009, 03:30 PM
|
|
Replies: 9
Views: 284
|
Forum: NEC
11-09-2009, 03:20 PM
|
|
Replies: 44
Views: 1,570
|
Forum: NEC
11-05-2009, 03:47 PM
|
|
Replies: 41
Views: 831
There is an exception for dwelling units from...
There is an exception for dwelling units from having a grounding electrode were fed by a single or multiwire BC.
But you still have to comply with the disconnecting means requirement in 225
225.31...
|
Forum: NEC
11-04-2009, 03:19 PM
|
|
Replies: 8
Views: 224
|
Forum: Lighting
11-04-2009, 03:17 PM
|
|
Replies: 24
Views: 887
|
Forum: Safety
11-03-2009, 08:18 PM
|
|
Replies: 7
Views: 474
|
Forum: NEC
11-03-2009, 06:59 PM
|
|
Replies: 11
Views: 348
There is a type of NM cable NM-C intended for...
There is a type of NM cable NM-C intended for this application, but its not common.
I would suggest PVC sch 80 with PVC FS boxes, run guard strips on each side to protect from chewing and damage.
|