Where are you considering using such a device?
Will it be a permanent installation?
What kind of load?
At our plant, temporary often becomes permanant.
I am not considering using such a device. The production employees like to use them. We have cord reels all over our plant that hang from the ceiling. They will plug a 6.75 hp shop vac and two industrial floor fans into one circuit. The circuit breaker will handle the load but the slip-ring in the cord reel, even though it's rated at 20 amps, will not. The cord reels are $400 each.
I just went out and looked at a couple of tri-taps on our shop floor, they are all rated 15a, 125 volt and UL listed. The load on one of them with the vaccum running is around 17-18 amps. I tried at one of our other locations putting 15a breakers on the existing 20a circuits so the breaker would trip instead of overloading the cord reel. After a few 20 minute drives just to reset a breaker, I decided that wasn't the best idea I ever had.
Maybe I just need to find tri taps that will burn up before the cord reel.:grin: