Good evening. I am a Seabee in Iraq and I have an issue with bonding vs grounding. I have 2 150Kw gen set's in series puttinf out 3 phase 4 wire 390v with a seperate ground wire. They are feeding a MDP. This MDP feed's the motor pool shop and the CHU's <sort of like work site trailer's> as well as other various building on site. Our Task Force Safety did an electrical inspection of the system and said the ground/neutral bar needed to be bonded at the CHU's and the metal braid in the wire's <200mm> needed to be used as the ground from the genset to the MDP. Also the ground rod's <earth ground> at each CHU was ineffective and ground needed to go back to the MDP as well as the MDP neutral/ground bar be bonded also. Also back a few year's ago a 30 ft trench was dug and <3> 9 ft ground rod's were buired to make an effective earth ground. This is almost impossable to do out here in the desert! OK so far? Now, When I went to bond the ground and neutral bar at the CHU, the main in the Pwr Pnl tripped. If I removed the ground wire and touched the ground and neutral bar's with a jumper it DIDN'T trip. Aas I understand it there are a total of 3 seperate grounding systems, and the only real way to fix it is to rewire from the genset's with a single ground to the MDP and ground it and bond it at the same time. Then carry the bonding at the MDP to the various buildings. Does this make sense to you? The TFS gent is a very demanding man. I explained what I felt was the problem and why we needed to do a rewire, but he said I was wrong. Is there any NEC that will help me here? Thank you for your help in advance.
R/
CE2 <SCW> Kennedy