250.64(e)

Status
Not open for further replies.

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
As I read 250.64(E), a bonding jumper need not be used at the panel end of a continuous metallic GEC raceway if the panel enclosure is also metallic.

Let the flames begin. ;)
 

RUWired

Senior Member
Location
Pa.
It seems that the panel itself takes care of bonding that end of the conduit.

I agree with your statement because 250.64 E says that the raceway needs to be continious. If you installed a raceway from the panel right up the "threaded hub" on a ground clamp, a jumper would not be needed.

Rick
 

RUWired

Senior Member
Location
Pa.
I think the hand book is showing a bonding bushing because there isn't a lock nut on the inside of the panel.

Rick
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I think I should point out that illustration showing 250.64(E) is from Mike Holt, not the NECH, the illustration showing the GES bonding is from the NECH.

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
do we all agree on this as fact. As simple of a question as this is I'm not sure we all agree? Is the EMT connector enough at the panel We all agree if the conduit isn't continuous to the electrode the GEC needs bonding, the problem is at the panel!

Eddie, the EMT connector would be sufficient in any case.

Roger
 