A AllNatural Member Dec 11, 2007 #1 We have a requirement to power a single 30A welder from a 40A circuit. The problem is - the 30A welder's power cord is furnished with a 60A plug. Can a 60A receptacle be installed on a 40A circuit and meet the NEC code?
We have a requirement to power a single 30A welder from a 40A circuit. The problem is - the 30A welder's power cord is furnished with a 60A plug. Can a 60A receptacle be installed on a 40A circuit and meet the NEC code?
480sparky Senior Member Location Iowegia Dec 11, 2007 #2 See Table 210.24 as well as 210.20 and 210.21.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Dec 11, 2007 #3 A single 60 amp receptacle is permitted on a 40 amp circuit. Look at 210.21(B)(1).
A AllNatural Member Dec 12, 2007 #4 Receptacle Sizing Receptacle Sizing Many thanks gentlemen. I read that, but wanted a more expert opinion. Jeff
Receptacle Sizing Receptacle Sizing Many thanks gentlemen. I read that, but wanted a more expert opinion. Jeff