B B henderson New member Feb 27, 2008 #1 resenty I was asked if a main disconect was required in the breaker panel in 1976 as required by nec
frizbeedog Senior Member Location Oregon Feb 27, 2008 #2 Simple answer is no. More info would help. :smile:
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Feb 27, 2008 #3 B henderson said: resenty I was asked if a main disconect was required in the breaker panel in 1976 as required by nec Click to expand... To my knowledge the NEC has never required a main disconnect to be INSIDE of any panel. I believe the NEC has always allowed the main to be in a separate enclosure/location.
B henderson said: resenty I was asked if a main disconect was required in the breaker panel in 1976 as required by nec Click to expand... To my knowledge the NEC has never required a main disconnect to be INSIDE of any panel. I believe the NEC has always allowed the main to be in a separate enclosure/location.
2 220/221 Senior Member Location AZ Feb 27, 2008 #4 Need more info. "Panel" is to vague. If the panel is the service and had more than 6 breakers or if it was in a separate building from the main service.....yes
Need more info. "Panel" is to vague. If the panel is the service and had more than 6 breakers or if it was in a separate building from the main service.....yes