Here are some pic.s from a very scientific test I performed a short time ago.

Testers used:
Ideal Circuit Tracer (Just the one piece)
Ideal Vol-Con (about 21 years old)
Fluke T2
Fluke 87
AWS Snap 8
GreenLee GT-11

....shown also is one partial roll of 14/3 NM



I stripped back both ends of the NM and jammed the black and white wires into a working outlet ~ the red and EGC are not connected to anything...using the Ideal Tracer to show that the recept is HOT:







Next...
We did NOT detect any voltage with the Vol-Con:


Next....
We sensed a voltage using the Fluke T2:


Next....
We sensed a voltage using the Fluke 87:


Next...
We did NOT detect any voltage with the Snap 8:


Finally....
We sensed a voltage on the red wire...on the end of the NM that was inserted into the recept. using the GreenLee GT-11: