POWER_PIG said:thanks again,
Pig
POWER_PIG said:thanks again,
Pig
infinity said:Switches do not required a bonding jumper for these types of covers.
iwire said:They do under the 2005 NEC.
infinity said:Receptacles won't require them either under the 2008 code if the cover has indented corners like a cover for a 1900 box.
infinity said:Do you mean receptacles?
iwire said:No I mean for switches, 404.9(B) requires that metal face plate to be grounded.
iwire said:Rob, Read (1) to 409.4(B) and notice that only applies to switches mounted to boxes (like a mud ring) not mounted to covers.
A switch mounted to a raised cover has to have a wire EGC running to it.
stickboy1375 said:but they allow a receptacle to to be installed in a raised cover without a pigtail, so why in the world would a switch not be allowed?
iwire said:No one has put in a proposal that made it?