I have seen CFL down lights recessed installed under canopy everywhere. They are obviously not listed for damp or wet location. I am wondering if the place under outdoor canopy is a damp location. What do you think?
 

stickboy1375

Senior Member
Location
Litchfield, CT
dahualin said:
I have seen CFL down lights recessed installed under canopy everywhere. They are obviously not listed for damp or wet location. I am wondering if the place under outdoor canopy is a damp location. What do you think?

Anything outdoor is a damp location. Anyhow, check out the definition of Location, Damp. it will answer your question.
 

Controls

Member
Location
North East
Article 100 Definitions: Location, Damp section.If you read it, canopies mentioned as part of damp locations. Not sure if this helps you. I am thinking that fixtures have to be listed for the areas (damp, wet, dry) where they are installed.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
mdshunk said:
What makes you think that CFL's are not okay for a damp location?
Especially reflector CFL's, which have a glass or plastic envelope around the actual lamp.
 

dahualin

Senior Member
I thought open CFL downlights are not listed for damp location. After checking some lighting catalogs, I found a lot of downlights are listed for damp/wet location. Thanks.
 