Running NMC

Status
Not open for further replies.

neutral

Senior Member
Location
Missouri
Hi
Would running nmc (approx. 6 #12 and 2 #10) on top of a basement wall below the floor joist be code compliant? The floor joist are sitting on a 2x6 plate and the basement wall is 10 inches thick. Could this be the same as using running boards? I have searched the 2005 code book but can't find anything that would support it
 
For what it's worth, I run cables up there all the time. The pressure treated sill plate is normally a 2x6 or 2x8 sitting on top of an 8" or 10" block wall. You have this 1-1/2" high space on top of the block wall to stash cables. I think this is a great place to run cables, if that is indeed what you're talking about:

joistdetail.jpg
 
Hi
Thanks for the replies. NMC I thought was non metalic cable or romex. Ive only been an electrician since 1962 so I'm still learning. I can use all the help I can get.

Thanks Charlie
 
mdshunk said:
Okay, I'll bite. Where did you get your hands on NMC cable?

NMC - Insulated conductors enclosed within an overall, corrosion resistant, nonmetallic jacket (from 334.2)

It is covered in the NEC but I have never heard of any wire manufacturers that actually make it.

I think the OP is referring to regular NM-B
 
mdshunk said:
For what it's worth, I run cables up there all the time. The pressure treated sill plate is normally a 2x6 or 2x8 sitting on top of an 8" or 10" block wall. You have this 1-1/2" high space on top of the block wall to stash cables. I think this is a great place to run cables, if that is indeed what you're talking about:

joistdetail.jpg

If so then he has bundling problems.
 
Hi
Why would running the cables on top of the basement wall be a bundling problem and approx. 50 cables coming down the wall to the two 200 amp distribution panels not be? What article covers bundling; I have searched the 2005 NEC book and can?t find anything, maybe I should go stay a night at a Holiday Inn.
Thanks Charlie.
 
neutral said:
Hi
Why would running the cables on top of the basement wall be a bundling problem and approx. 50 cables coming down the wall to the two 200 amp distribution panels not be? What article covers bundling; I have searched the 2005 NEC book and can?t find anything, maybe I should go stay a night at a Holiday Inn.
Thanks Charlie.

Bundling has been being enforced for last 6 to 10 years.I as probly others are wondering just when did you do your last home ?Many things have changed in the last 20.I have not none a house in last 5 years,ok one.Many things now that passed 10 years ago never fly now.We have afci,gfci,bundling.I myself fould find it hard to go wire a house monday without talking to a local residential guy.Go check how many conductors can be ran together in the charts,you might be in for a shock.
 
neutral said:
Hi
Why would running the cables on top of the basement wall be a bundling problem and approx. 50 cables coming down the wall to the two 200 amp distribution panels not be? What article covers bundling; I have searched the 2005 NEC book and can?t find anything, maybe I should go stay a night at a Holiday Inn.
Thanks Charlie.

Hi. Welcome to the forum. Lots of guys around here call "romex" by the letters NMC and they mean Non Metallic Cable, but the "C" actually means "corrosion resistant". It's a common misnomer.
As far as "bundling", take a look at 310.15(B)(2)(a) in the NEC. :smile:
 
wbalsam1 said:
Hi. Welcome to the forum. Lots of guys around here call "romex" by the letters NMC and they mean Non Metallic Cable, but the "C" actually means "corrosion resistant". It's a common misnomer.
As far as "bundling", take a look at 310.15(B)(2)(a) in the NEC. :smile:
Hey sometimes I think I'm a misnomer,

Charlie
 
I've never seen any new NMC. I've seen old, already installed, NMC. The old-timer that trained me called it "barn cable", because that's how it was mostly used. I really don't see how it was any different than UF.
 