MWhitt said:If i understand this section correctly, it is permitted to use MC cable in patient care areas for lighting as long as the fixtures are above 71/2 feet. Does anyone have any experience with this application?
kfenn22 said:I have used this for OR and ER rooms. The way I see it, you do not have to have the light fixtures on an GFI/ISO circuit in patient care area if the ceiling is higher then 7.5 feet.... I prefer not to use the MC in hospitals, unless it is a whip...
According to Article 517.13, do light fixtures above 7 ? feet require a redundant ground for cable sheath, or does the exception 517.13 (B)(2) allow you to use a non-listed cable for the lights?
Panel Response: The sheath of the cable is required to be listed as equipment grounding return path, however, an insulated copper-grounding conductor is not required.
M. D. said:Not that Chris needs it but these folks also agree with his position.
http://www.nema.org/stds/fieldreps/askMikeForister/upload/MichIAEI12.05.doc
MC is Metal-Clad Cable see article 330. AC is Armored Cable see 320. Armored cables sheath is recognized as an EGC because of an aluminum runner along it's sheath, standard MC's sheath was not recognized as an EGC.kfenn22 said:maybe I'm getting my terms mixed up... what is the difference between MC and a Metallic armor cable?
steve66 said:If this is on an emergency circuit, what about 517.30(C)(3)(3)(d)??
"Listed flexible metal raceways...where necessary for flexible connection to equipment"
Does everyone agree that a light fixture needs a flexible connection???? Just wondering.
kfenn22 said:Ok, I understand the difference now, but how do you identify between the two when it is installed, with out opening it up? does ac have the green shielding? How about the MC with the GEC in it? is that Green as well.....
C3PO said:Southwire's version of the "new" MC cable is MCap. It has writing on the plastic inside that says "armour is equipment grounding conductor" or something like that.
roger said:Note; there is HCFC that is not green.