I was hoping for a suggestion on a situation I have at a on going job.
Senerio: 5 # 10 AWG stranded copper conductors going from the 1st floor to the 4th floor in 3/4" emt.
Total length of vertical conductors is less than 100 feet, but the conductors want to pull back down.
In hindsight I probably should have used solid conductors, but I didn't.
I looked for a grommet to support the cables, but only came up with devices for larger conductors.
The wires go into a 4" X 2-1/8 junction box, so I dont have alot of room.
In your experiences have you come across a similar problem?
And if so, how did you support the conductors, The inspector in the area is "by the book".
I thought about kellums grips, but was concerned that these were only rated for cables, not wire bundles.
Any thoughts or suggestions would be greatly appreciated.
Thanks for your time.
Joe Villani
Senerio: 5 # 10 AWG stranded copper conductors going from the 1st floor to the 4th floor in 3/4" emt.
Total length of vertical conductors is less than 100 feet, but the conductors want to pull back down.
In hindsight I probably should have used solid conductors, but I didn't.
I looked for a grommet to support the cables, but only came up with devices for larger conductors.
The wires go into a 4" X 2-1/8 junction box, so I dont have alot of room.
In your experiences have you come across a similar problem?
And if so, how did you support the conductors, The inspector in the area is "by the book".
I thought about kellums grips, but was concerned that these were only rated for cables, not wire bundles.
Any thoughts or suggestions would be greatly appreciated.
Thanks for your time.
Joe Villani