gfci's dont need an equipment ground to operate. they work by sensing a current unbalance.
Do you have an example aside from the noise mentioned in you link?gar said:In a sense GFCI is the wrong name for this device because it is not necessary for the current to flow to or thru ground. A current from any source that produces a difference in the hot relative to neutral currents will cause the GFCI to trip.
chris kennedy said:Do you have an example aside from the noise mentioned in you link?
76nemo said:....#2, and I think this is where the confusion may lie, (you're either with me or not quogue), the GFCI device must have a ground in order to be tested with an EXTERNAL tester. The test button will work w/o a ground, but with an EXTERNAL tester, a ground must be present in order for YOUR tester to open the circuit....
480sparky said:Take a standard, 3-wire GFI plug in tester and stick it into a non-grounded GFI-protected receptacle. The tester WILL NOT TRIP the GFI. And I agree with 76 here...
480sparky said:I think that is where the misconception comes from.
LarryFine said:However, I would like to add that the electrical supply system itself must have a grounded circuit conductor, such as our ever-popular neutral, for it to work.
Agreed .crossman said:Depends on what you mean by "to work". A GFCI breaker or receptacle will trip whenever the imbalance through the CT exceeds whatever level the manufacturer has built into the device, and a grounded circuit conductor at the supply is not a prerequisite for this tripping to occur.
crossman said:Depends on what you mean by "to work". A GFCI breaker or receptacle will trip whenever the imbalance through the CT exceeds whatever level the manufacturer has built into the device, and a grounded circuit conductor at the supply is not a prerequisite for this tripping to occur.
All you need is a second circuit that is faulted to the plumbing. No ground bond needed.dbuckley said:Whereas what you say is absolutely true, its pretty hard to get a current imbalance without the supply being grounded. In particular, a single fault such as a hot to plumbing touch would not cause any current to flow in the absence of a ground bond somewhere. Such a supply would have two hots and no neutral.
dbuckley said:Whereas what you say is absolutely true, its pretty hard to get a current imbalance without the supply being grounded. In particular, a single fault such as a hot to plumbing touch would not cause any current to flow in the absence of a ground bond somewhere. Such a supply would have two hots and no neutral.
What I mean by "to work" is to protect a human being who is in contact with the earth (or other grounded surface) from electrocution due to accidental contact with an energized conductor or equipment.crossman said:Depends on what you mean by "to work". A GFCI breaker or receptacle will trip whenever the imbalance through the CT exceeds whatever level the manufacturer has built into the device, and a grounded circuit conductor at the supply is not a prerequisite for this tripping to occur.LarryFine said:However, I would like to add that the electrical supply system itself must have a grounded circuit conductor, such as our ever-popular neutral, for it to work.