Isn't there a vertical limit?
Alot of times plan specifications will have a limit to the length of conduit between boxes. I know in the past I have worked on projects that had a specification of no more than 100' between pull points.
Chris
As far as I know that was never in the NEC.Hi,
Thanks for al the replies. I think I saw in an old code book where there used to be a article that covered this but since I dont have an old mid 90's code book then I cant quote it.
Again, thanks.
GW
And I think that standard goes on to say that you deduct 30' from that 100' for every 90.I think 100' is also a 'BICSI' standard for data / com etc.
Yup, Lcdrwalker is correct. Vertical conductors require support at given intervals depending on the conductor size. That would make a straight vertical run of conduit still need pull boxes.
That is more than 360?. 3-90? is 270?, add 60? gets you to 330? and only leaves you 30? for the rest of the offsets. You say there were 'some' which leads me to think that there were more than 4 at 22??. If memory serves me correctly, you kick 22?? in both directions for an offset for 45? for each offset. You have run over if this is the case. :smile:. . . i meant it looked like three 90's a 60 and some offsets that were probably 30. . .
Good advice. Also, the manufacturers will publish pulling charts for their larger cables and wire. You then have to calculate the pulling tensions with and without lube to see if the wire or cable will withstand the pull without damage. :smile:If you are at a large plant, see if the plant has a spec requirement book for Electrical work, Div16, or however they divvy up the working classifications.