You could do it with (4) sets of 3/0 75 deg conductors.

Roger
 
I was trying to get away with only 2 conduit runs. Sorry for not explaining... Also is it possible to run 2 sets of Service conductors in the same conduit.(As seen in a separate thread in NEC Section)

As long as you adjust the conductors ampacity per table 310.15(B)(2)(a)

Roger
 
Unless the major portion of your load is non-liner, then your neutral would count as currrent carying and you would need to look at the calculated load.
 
Thanks for adding that point, Gus. In some cases, those with small neutral loads, that section will require a larger grounded conductor than does the load calculation.

I come up with a Neutral (Unbalanced load) of approximately 280 Amps. So if I call it 400 Amps and run two 4/0s (One per run) it will keep me at 7 wires per run and should not be a problem with conductor ampacity. The majority of my loads is a 200Amp 3 Phase Heater and about a dozen 3 phase motors Most of which are 30FLA and 2-3 are 5.5 FLA and a little HVAC(not 3 phase). Does anyone see a problem with this?
 