Is there an EASY way to understand building types for NM use? I've read the annex E and it's not so clear to me. Inspector today wants a letter from the architect......
Is there an EASY way to understand building types for NM use? I've read the annex E and it's not so clear to me. Inspector today wants a letter from the architect......
See 334.10 and 334.12
OP did ask for "easy way" but did not give parameters on what "easy" would mean.![]()
Just wanted to point out that 334.10(3) says that "Other structures permitted to be of Types III, IV, and V construction...."
which I believe means that even though a structure was built with steel and concrete typical of Type I and II, if the Architect or Engineer can
determine that the structure "could" have been or would be permitted to have been built as a Type III, IV, and V....then type NM cable
may be permitted.
I disagree with this. The Architect determines the building construction type. Once it is classified you are limited to that classification for anything that is allowed in that building type. "structures" means structures other than dwelling units as directed in part (1) and (2).
But if you were going to upgrade the construction method why not upgrade electrical, HVAC, etc. to sort of match, like you said someday someone else may think it is a fit for some other application then finds out some parts of it are not.I concur with sparkyHC, few lol. The decision to make some components of the building higher quality (i.e. more fire resistant) than required by building code should not automatically require more expensive electrical wiring to be used.
The only large hypothetical issue, IMHO, comes if a later owner decides on a building occupancy type that requires Type 1 or 2 construction assuming that the electrical was also done to that higher standard.
Sent from my XT1585 using Tapatalk
I agree with the "why not?" But that does not make it code required.But if you were going to upgrade the construction method *why not* upgrade electrical, HVAC, etc. to sort of match, like you said someday someone else may think it is a fit for some other application then finds out some parts of it are not.
Just wanted to point out that 334.10(3) says that "Other structures permitted to be of Types III, IV, and V construction...."
which I believe means that even though a structure was built with steel and concrete typical of Type I and II, if the Architect or Engineer can
determine that the structure "could" have been or would be permitted to have been built as a Type III, IV, and V....then type NM cable
may be permitted.
I disagree with this. The Architect determines the building construction type. Once it is classified you are limited to that classification for anything that is allowed in that building type. "structures" means structures other than dwelling units as directed in part (1) and (2).
what if...
what if you decided to build a small "B" use building, say 1000 square feet. You could easily build this structure with Type IV construction and install NM. If of course
for some reason you were worried about losing your investment and decided to build this as a Type II would you still be allowed to install NM cable?
I would argue, Yes, because even though you built this building as a Type II, you were "permitted" to build this with Type IV construction.
Still disagree? (and I do agree with you that if I tried to apply this I would get a letter from an Architect)