Question 480V Single Phase with Grounded Leg

I am looking for a way create a 480V single phase feeder with one leg grounded. The load is 48KVA. I am trying to create this from a 480/277V, three phase feeder. Does anyone make a 50KVA, 480V-480V single phase transformer ?

Thanks in advance!
__________________
Jeff
"Watt's Up !!"
  #2  
Old 11-17-2009, 03:44 PM
bob's Avatar
bob bob is offline
Senior Member
 
Join Date: Feb 2003
Location: Nashville
Posts: 2,063
Default

Quote:
Originally Posted by jbt260 View Post
I am looking for a way create a 480V single phase feeder with one leg grounded. The load is 48KVA. I am trying to create this from a 480/277V, three phase feeder. Does anyone make a 50KVA, 480V-480V single phase transformer ?

Thanks in advance!
Why do you have to have one leg grounded? Take 2 of the 3 phases plus an egc and you have 480 volts single phase.
  #3  
Old 11-17-2009, 05:00 PM
jbt260 jbt260 is offline
Member
 
Join Date: Mar 2004
Location: Ohio
Posts: 71
Default

Sorry for lack of info. I have to re-feed an existing roadway lighting circuit that is 480V single phase with a grounded leg. The leg is grounded at every light pole.
__________________
Jeff
"Watt's Up !!"
  #4  
Old 11-17-2009, 07:55 PM
bob's Avatar
bob bob is offline
Senior Member
 
Join Date: Feb 2003
Location: Nashville
Posts: 2,063
Default

Quote:
Originally Posted by jbt260 View Post
Sorry for lack of info. I have to re-feed an existing roadway lighting circuit that is 480V single phase with a grounded leg. The leg is grounded at every light pole.
I am not sure that meets the NEC groounding requirements. I believe you need a EGC to each pole rather that using the neutral. Maybe someone will confirm this.
  #5  
Old 11-17-2009, 08:34 PM
Cavie's Avatar
Cavie Cavie is offline
Senior Member
 
Join Date: Mar 2006
Location: SW Florida
Posts: 1,856
Default

480 2 wire single phase. 1 hot 1 neutral and a ground. Very common in street lighting. Something I learned after being an electrican for 40 years.
__________________
Unlimited Electric Contractor/Standard Electric Inspector/Traffic Signal Inspector/Highway Lighting and Level One Traffic Signal Installer.

I know you believe that you understand what you think I said but I'm sure you realize that what you heard is not what I meant.
  #6  
Old 11-17-2009, 08:47 PM
brian john brian john is offline
Senior Member
 
Join Date: May 2003
Posts: 6,121
Default

Quote:
Originally Posted by Cavie View Post
480 2 wire single phase. 1 hot 1 neutral and a ground. Very common in street lighting. Something I learned after being an electrican for 40 years.
480 VAC Single phase is one hot, one grounded conductor and one EGC. I would think?
  #7  
Old 11-17-2009, 08:37 PM
Cavie's Avatar
Cavie Cavie is offline
Senior Member
 
Join Date: Mar 2006
Location: SW Florida
Posts: 1,856
Default

Quote:
Originally Posted by jbt260 View Post
Sorry for lack of info. I have to re-feed an existing roadway lighting circuit that is 480V single phase with a grounded leg. The leg is grounded at every light pole.
Check with your local POCO. Why arn't they supplying you?
__________________
Unlimited Electric Contractor/Standard Electric Inspector/Traffic Signal Inspector/Highway Lighting and Level One Traffic Signal Installer.

I know you believe that you understand what you think I said but I'm sure you realize that what you heard is not what I meant.
  #8  
Old 11-18-2009, 12:31 AM
benaround benaround is offline
Senior Member
 
Join Date: Mar 2004
Location: Arizona
Posts: 3,909
Default

Quote:
Originally Posted by jbt260 View Post
. The leg is grounded at every light pole.
jbt, What does this mean?
__________________
Frank Arizona,USA
  #9  
Old 11-18-2009, 07:17 AM
mattsilkwood mattsilkwood is offline
Senior Member
 
Join Date: Dec 2006
Location: missouri
Posts: 466
Default

Someone please tell me if im wrong, but wouldn't a regular 480v circuit (480 L1-L2) do the same thing? the light isnt going to know if one conductor is grounded, and you're not going to bond the poles.
  #10  
Old 11-18-2009, 08:13 AM
jbt260 jbt260 is offline
Member
 
Join Date: Mar 2004
Location: Ohio
Posts: 71
Default

A tfmr manufacturer came up with a solution for a 50KVA, 480V-480V, single phase transformation. They suggest using two 25KVA, 240x480V Primary, 120/240V Secondary, single phase transformers. You wire the primaries in parallel for 480V. You wire the secondaries in series for 480V. See attached diagram. Any thoughts are welcome !
Attached Images
File Type: jpg 480-480.jpg (15.5 KB, 36 views)
__________________
Jeff
"Watt's Up !!"
Closed Thread

CEU Banner Home Page

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 10:08 PM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.