I am looking for a way create a 480V single phase feeder with one leg grounded. The load is 48KVA. I am trying to create this from a 480/277V, three phase feeder. Does anyone make a 50KVA, 480V-480V single phase transformer ?
Thanks in advance!
__________________
Jeff "Watt's Up !!" |
|
#2
|
||||
|
||||
|
Why do you have to have one leg grounded? Take 2 of the 3 phases plus an egc and you have 480 volts single phase.
|
|
#3
|
|||
|
|||
|
Sorry for lack of info. I have to re-feed an existing roadway lighting circuit that is 480V single phase with a grounded leg. The leg is grounded at every light pole.
__________________
Jeff "Watt's Up !!" |
|
#4
|
||||
|
||||
|
I am not sure that meets the NEC groounding requirements. I believe you need a EGC to each pole rather that using the neutral. Maybe someone will confirm this.
|
|
#5
|
||||
|
||||
|
480 2 wire single phase. 1 hot 1 neutral and a ground. Very common in street lighting. Something I learned after being an electrican for 40 years.
__________________
Unlimited Electric Contractor/Standard Electric Inspector/Traffic Signal Inspector/Highway Lighting and Level One Traffic Signal Installer. I know you believe that you understand what you think I said but I'm sure you realize that what you heard is not what I meant. |
|
#6
|
|||
|
|||
|
480 VAC Single phase is one hot, one grounded conductor and one EGC. I would think?
|
|
#7
|
||||
|
||||
|
Check with your local POCO. Why arn't they supplying you?
__________________
Unlimited Electric Contractor/Standard Electric Inspector/Traffic Signal Inspector/Highway Lighting and Level One Traffic Signal Installer. I know you believe that you understand what you think I said but I'm sure you realize that what you heard is not what I meant. |
|
#8
|
|||
|
|||
|
jbt, What does this mean?
__________________
Frank Arizona,USA |
|
#9
|
|||
|
|||
|
Someone please tell me if im wrong, but wouldn't a regular 480v circuit (480 L1-L2) do the same thing? the light isnt going to know if one conductor is grounded, and you're not going to bond the poles.
|
|
#10
|
|||
|
|||
|
A tfmr manufacturer came up with a solution for a 50KVA, 480V-480V, single phase transformation. They suggest using two 25KVA, 240x480V Primary, 120/240V Secondary, single phase transformers. You wire the primaries in parallel for 480V. You wire the secondaries in series for 480V. See attached diagram. Any thoughts are welcome !
__________________
Jeff "Watt's Up !!" |
![]() |