![]() I have done similar installations and to tell the truth never gave it much thought but,.. would the structure to the right (post with required receptacle outlet) require a disconnect ? I think it meets the definition of a "structure" and as such would require one . I also think it is an outbuilding as described in the exception to 225.36. Next question ;does the snap switch have to be at or near the structure served? I think it does In the area where I work this would not be tagged as a 225.31 violation. Has anyone ever been tagged for this? stories and Opinions Please.
__________________
"America will never be destroyed from the outside. If we falter and lose our freedoms, it will be because we destroyed ourselves." Abraham Lincoln |
|
#2
|
||||
|
||||
|
Wow! that is some back yard. In the area I am from, there would probably be about a 1000 homes in that picture.
From what I can see by your photo, the receptacle would be premitted as your disconnecting means. Nice picture..."a picture is worth a thousand words."
__________________
Instructor, Industry Advocate |
|
#3
|
||||
|
||||
|
Thanks for the reply Pierre, I'm not sure the receptacle provides a disconnecting means as to disconnect the ungrounded conductors that supply the structure though
If this structure were a garden shed with a receptacle installed would it not require a disconnect??
__________________
"America will never be destroyed from the outside. If we falter and lose our freedoms, it will be because we destroyed ourselves." Abraham Lincoln |
|
#4
|
||||
|
||||
|
I think the NEC requires a disconnecting means.
A while back I installed four 30 amp 208 volt branch circuits to receptacles on a single post at a fair grounds. Once the job was underway and I really started to think about it I think I was in violation of 225.30 225.31 250.32(A) In the end the inspector felt it was fine as it was.
__________________
Bob |
|
#5
|
||||
|
||||
|
Quote:
225.30 in the case of this post, there seems to be only one circuit per post 225.31 The receptacle could be the disconnecting means 250.32(A) The exception to (A) would most likely suffice here, meaning no grounding electrode would be required by NEC.
__________________
Instructor, Industry Advocate |
|
#6
|
||||
|
||||
|
Quote:
Do you have receptacles rated as service equipment per 225.36? Do you have any receptacles that meet the requirements of 225.38? In my opinion the receptacle in the picture can serve as the disconnecting means for the pump but by the letter of the code it can not serve as the disconnecting means for this 'structure'.
__________________
Bob |
|
#7
|
||||
|
||||
|
Quote:
Bob , It was and is a violation and I think most of us know why . Who cares how the inspector "felt" he has limited liability . I think this is a great example of why there should be a disconnect. Were they at least labeled as to where the ocpd might be found??? The purpose of the electrical code is the practical safeguarding of persons and property from the hazards arising from the use of electricity. I don't think a disconnect is an outrageous thing to ask for. There have been times that a time clock was used as a pool disconnect ... house locked and I have to replace the time clock motor ,... after about the third or second time ,I concluded that the time clock itself requires a disconnect . a little off subject ,.. but not really . most of the injuries to us electricians can be prevented by the flip of a switch, .. about 13 a day show up at burn centers.
__________________
"America will never be destroyed from the outside. If we falter and lose our freedoms, it will be because we destroyed ourselves." Abraham Lincoln |
|
#8
|
||||
|
||||
|
Quote:
That said I am not going to lose sleep over it, as you can see the 'accepted trade practice' is not to include disconnects at structures that only are there to support the receptacle.
__________________
Bob |
|
#9
|
|||
|
|||
|
Read through 680 for Storable Pools. How deep is the pool (see definition of a storable pool)? 680.7, 680.12 for disconnecting means. 680.21(A)(1)&(5) minimum equipment gound and length of cord, 680.22(A)(5) GFCI within 10', 680.22(A)(1,2,3,4) for pump 5' to 10' from pool and 680.26(B) for equipotential bonding.
Last edited by RAYMFL; 09-21-2007 at 05:23 PM. |
|
#10
|
||||
|
||||
|
Quote:
It is a matter of the NEC defining that post the receptacle is on as a structure.
__________________
Bob |
![]() |