Quote:
Originally Posted by A-1Sparky View Post
It hasn't been inspected yet, but I didn't see the need for a GFI mounted on the side of an island. Island countertop, yes. But this would be more of a convenience outlet.
Technically, if you can place something on the island countertop and plug it into the receptacle without an extension cord, that receptacle is serving the countertop.
__________________
Cheers and Stay Safe,

Marky the Sparky

OSHA 1910.304(g)(2)(iv) "One phase conductor of a multiphase system where one phase is grounded shall be grounded"
  #12  
Old 11-03-2009, 03:27 PM
stars13bars2 stars13bars2 is offline
Senior Member
 
Join Date: Feb 2003
Posts: 190
Default

What else would you need a receptacle on the side of an island for anyway?
  #13  
Old 11-03-2009, 03:42 PM
electricmanscott's Avatar
electricmanscott electricmanscott is offline
Senior Member
 
Join Date: Feb 2003
Location: I Live in Holden Massachusetts, if you're in the area, look me up
Posts: 6,588
Default

You are required to install a receptacle on the island and it's sole purpose is to serve the counter.
__________________
There are two kinds of people - those smart enough to know they don’t know, and those dumb enough to insist they do.-----Margery Eagan

Open shop since 1988
  #14  
Old 11-03-2009, 05:04 PM
infinity's Avatar
infinity infinity is offline
Moderator
 
Join Date: Jul 2003
Location: New Jersey
Posts: 12,587
Default

Quote:
Originally Posted by K8MHZ View Post
Technically, if you can place something on the island countertop and plug it into the receptacle without an extension cord, that receptacle is serving the countertop.
If the receptacle is more than 12" below the top of the countertop it does not count as serving the island. 210.52(C)(5). I would guess that an applicance with a 2' cord could still reach an outlet that is more than 12" below the countertop surface.
__________________
Rob

Moderator
  #15  
Old 11-03-2009, 05:24 PM
1793's Avatar
1793 1793 is offline
Senior Member
 
Join Date: Jul 2004
Location: Kentucky
Posts: 1,573
Default

Quote:
Originally Posted by electricmanscott View Post
You are required to install a receptacle on the island and it's sole purpose is to serve the counter.
Quote:
Originally Posted by infinity View Post
If the receptacle is more than 12" below the top of the countertop it does not count as serving the island. 210.52(C)(5). I would guess that an applicance with a 2' cord could still reach an outlet that is more than 12" below the countertop surface.
As I see it, one receptacle can't serve both the requirement for countertop(s) and convience if more that 12" below the countertop.
__________________
Norb
My Boss is a Tyrant and my Employee is an Idiot.
  #16  
Old 11-03-2009, 05:36 PM
raider1's Avatar
raider1 raider1 is offline
Moderator
 
Join Date: Jun 2005
Location: North Logan, Utah
Posts: 6,276
Default

Quote:
Originally Posted by 1793 View Post
As I see it, one receptacle can't serve both the requirement for countertop(s) and convience if more that 12" below the countertop.
If the receptacle is more than 12" below the countertop then it can't count as the required receptacle for the countertop. (See the exception to 210.52(C)(5))

Chris
__________________
2010 Chief Moderator
  #17  
Old 11-03-2009, 05:47 PM
1793's Avatar
1793 1793 is offline
Senior Member
 
Join Date: Jul 2004
Location: Kentucky
Posts: 1,573
Default

Quote:
Originally Posted by raider1 View Post
If the receptacle is more than 12" below the countertop then it can't count as the required receptacle for the countertop. (See the exception to 210.52(C)(5))

Chris
That is what I was trying to say. One receptacle is required and can't be more that 12" below the countertop. So, if you want the receptacle lower you would need to install a second receptacle.
__________________
Norb
My Boss is a Tyrant and my Employee is an Idiot.
  #18  
Old 11-03-2009, 05:49 PM
raider1's Avatar
raider1 raider1 is offline
Moderator
 
Join Date: Jun 2005
Location: North Logan, Utah
Posts: 6,276
Default

Quote:
Originally Posted by 1793 View Post
That is what I was trying to say. One receptacle is required and can't be more that 12" below the countertop. So, if you want the receptacle lower you would need to install a second receptacle.
OK Got it.

Chris
__________________
2010 Chief Moderator
  #19  
Old 11-03-2009, 06:24 PM
infinity's Avatar
infinity infinity is offline
Moderator
 
Join Date: Jul 2003
Location: New Jersey
Posts: 12,587
Default

Quote:
Originally Posted by electricmanscott View Post
You are required to install a receptacle on the island and it's sole purpose is to serve the counter.
Quote:
Originally Posted by infinity View Post
If the receptacle is more than 12" below the top of the countertop it does not count as serving the island. 210.52(C)(5). I would guess that an applicance with a 2' cord could still reach an outlet that is more than 12" below the countertop surface.


Quote:
Originally Posted by 1793 View Post
As I see it, one receptacle can't serve both the requirement for countertop(s) and convience if more that 12" below the countertop.

Quote:
Originally Posted by K8MHZ View Post
Technically, if you can place something on the island countertop and plug it into the receptacle without an extension cord, that receptacle is serving the countertop.
My response was to K8MHZ's response for a test to see if a receptacle is actually serving a counter top. If the receptacle is more than 12" below the countertop surface his test is no longer correct.
__________________
Rob

Moderator
  #20  
Old 11-05-2009, 06:37 AM
A-1Sparky A-1Sparky is offline
Senior Member
 
Join Date: Jan 2009
Location: Upstate New York
Posts: 150
Default

This receptacle is more than 12" below the countertop. I thought that it would meet the requirement for an island recept., but wouldn't have to have GFI protection. I guess I need a second recept.
__________________
Life's the knife and I'm the scar!
Closed Thread

CEU Banner Home Page

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 12:49 PM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.