#11
|
|||
|
|||
|
When I do inspections I use my plastic pen to move wires in a box. Its not fool proof but it helps.
__________________
Rick Napier Inspector and Instructor |
|
#12
|
||||
|
||||
|
Quote:
I believe that is a jurisdictional issue. Where we work, the service can be energized as soon as it is completed, even before the roughing starts. Many contractors will try to do this to eliminate the need for temp power.
__________________
Instructor, Industry Advocate |
|
#13
|
||||
|
||||
|
It is, and they try it here too, but we're trying to keep everyone safe.
__________________
I can build anything you want if you draw a picture of it on the back of a big enough check. There's no substitute for hard work....but that doesn't mean I'm going to give up trying to find one. John Childress Electrical Inspector IAEI / CEI / C10 Certified Electrical Inspector |
|
#14
|
||||
|
||||
|
Quote:
![]() Protecting all if they need it or not. ![]() We would get a service inspection and engergize that, I don't think there is anything in the NEC to prohibit that regardless of what may or may not be done.
__________________
Bob |
|
#15
|
||||
|
||||
|
Quote:
And by the above, I think what you mean is you enforce the code. Thanks for that as well.
__________________
Moderator-Washington State Ancora Imparo |
|
#16
|
||||
|
||||
|
Quote:
![]() Just trying to keep Mr. Smith from being the late Mr. Smith. I bet that most of us here have a story of how we got shocked and most of them will contain the comment, or one like it, "I didn't know it was hot."
__________________
I can build anything you want if you draw a picture of it on the back of a big enough check. There's no substitute for hard work....but that doesn't mean I'm going to give up trying to find one. John Childress Electrical Inspector IAEI / CEI / C10 Certified Electrical Inspector |
|
#17
|
||||
|
||||
|
Around here, we can request a service inspection, which requires a complete electrode system, panel EGCs and groundeds made up, and a single-receptacle outlet (such as laundry) with GFCI protection.
While I'm not sure if it's required, I also make up all my device and equipment boxes, the EGCs and groundeds. Plus, I like to prepare the ungrounded wires and pigtails for trim-out at this time.
__________________
Code references based on 2005 NEC Larry B. FineElectrical Contractor Richmond, VA |
|
#18
|
||||
|
||||
|
Quote:
ROFLMAO Reinforcing the old stereotype
__________________
I'm an Inspector, what do I know? |
|
#19
|
|||
|
|||
|
Quote:
|
|
#20
|
|||
|
|||
|
Here we get power on the service inspection.
My practice has been to shut down all circuits and the main for rough in unless the need exists for a receptacle. In that case it would be a single receptacle circuit, the rest would be off. Until I meet an inspector I don't like, the above will be the case.
__________________
Cheers and Stay Safe, Marky the Sparky OSHA 1910.304(g)(2)(iv) "One phase conductor of a multiphase system where one phase is grounded shall be grounded" |
![]() |