I have been to several homes that I see single thhn conductors running in the walls. I have always told my customers that the wires must be in conduit or romex but I can’t find a code section that states that.
|
|
#2
|
|||
|
|||
|
Section 300.3(A) of the NEC...
__________________
Bryan P. Holland, ICC Electrical Code Official CBO, Plans Examiner, Inspector, Instructor Secretary - IAEI Florida Gulf Coast Division Secretary - BOAF Gulf Coast Chapter |
|
#3
|
||||
|
||||
|
Eq Ground conductors would be ok. I agree that circuits should be bundled together.
__________________
John, |
|
#4
|
||||
|
||||
|
EGC for what type of application?
__________________
Moderator-Washington State Ancora Imparo |
|
#5
|
||||
|
||||
|
I have, in the past, run a single conductor to a receptacle to establish an EG. I used 250.130 C (1) as my reference.
__________________
Norb My Boss is a Tyrant and my Employee is an Idiot. |
|
#6
|
|||
|
|||
|
Me too, I'd trust that more than putting a GFI there, on a two wire circuit. It's best for impedence if the EGC is ran with the ungrounded. But the exception allows the single conductor to be ran for this purpose. But this post is funny,,,,,your customers have to tell you how to do a job?
|
|
#7
|
||||
|
||||
|
Thanks, could not cite the ref off the top of my head.