Default LFMC fittings - direct buried

I know many brands of LFMC are listed for direct burial. However, I cannot find any fittings that are listed for direct burial.

I am trying to come out of a large jbox, below grade, and use flex conduit to avoid tree roots and hit a receptacle above grade. It has been recommended to me by a P.E. to use LFMC for this application.

Is LFMC the right conduit to use, and if so, who makes fittings listed for direct burial?

A little help for this lowly E.I.T., please.
  #2  
Old 11-02-2009, 07:58 PM
benaround benaround is offline
Senior Member
 
Join Date: Mar 2004
Location: Arizona
Posts: 3,909
Default

How do you have access to the j-box below grade ?
__________________
Frank Arizona,USA
  #3  
Old 11-02-2009, 08:14 PM
jbelectric777 jbelectric777 is offline
Senior Member
 
Join Date: Nov 2006
Location: New Jersey
Posts: 122
Default

BURIED JUNCTIONS!!!!! at this point it sounds like anything you do will be an improvement.....
  #4  
Old 11-02-2009, 08:17 PM
chris kennedy's Avatar
chris kennedy chris kennedy is offline
Senior Member
 
Join Date: Aug 2006
Location: Miami Fla.
Posts: 5,701
Default

Read the exception to 314.29 and grab a shovel.
  #5  
Old 11-02-2009, 08:30 PM
benaround benaround is offline
Senior Member
 
Join Date: Mar 2004
Location: Arizona
Posts: 3,909
Default

Caligula,

Lfmc fittings must be listed, I'm not 100% sure if d.b. is part of the listing.
__________________
Frank Arizona,USA
  #6  
Old 11-03-2009, 10:46 AM
raider1's Avatar
raider1 raider1 is offline
Moderator
 
Join Date: Jun 2005
Location: North Logan, Utah
Posts: 6,276
Default

According to the UL white book conduit fitting listed for direct bury should be marked by either direct bury or DB.

Chris
__________________
2010 Chief Moderator
  #7  
Old 11-03-2009, 03:42 PM
Caligula Caligula is offline
Junior Member
 
Join Date: Mar 2009
Posts: 21
Default

Clarification, just for the record, by "jbox below grade" I mean an ingrade box, with a top, like a quazite box.....
  #8  
Old 11-03-2009, 04:52 PM
chris kennedy's Avatar
chris kennedy chris kennedy is offline
Senior Member
 
Join Date: Aug 2006
Location: Miami Fla.
Posts: 5,701
Default

Quote:
Originally Posted by Caligula View Post
Clarification, just for the record, by "jbox below grade" I mean an ingrade box, with a top, like a quazite box.....
Here is the NEC definition for the record.

Quote:
Handhole Enclosure.
An enclosure for use in underground systems, provided with an open or closed bottom, and sized to allow personnel to reach into, but not enter, for the purpose of installing, operating, or maintaining equipment or wiring or both.
  #9  
Old 11-03-2009, 06:28 PM
Pierre C Belarge's Avatar
Pierre C Belarge Pierre C Belarge is offline
Senior Member
 
Join Date: Mar 2006
Location: Westchester County, New York
Posts: 7,791
Default

I do not see where LFMC fittings are suitable for direct burial.

Art 356, LFNC-B fittings are listed for direct burial, but the straight fitting only. 356.42.
__________________
Instructor, Industry Advocate
  #10  
Old 11-04-2009, 05:37 PM
Caligula Caligula is offline
Junior Member
 
Join Date: Mar 2009
Posts: 21
Default

Quote:
Originally Posted by Pierre C Belarge View Post
I do not see where LFMC fittings are suitable for direct burial.

Art 356, LFNC-B fittings are listed for direct burial, but the straight fitting only. 356.42.
By 356.42, any LFNC fitting would be OK for direct burial, while only LFNC specifically listed for direct burial is allowed. Seems inconsistent.

Thanks guys.
Closed Thread

SpecialBanner1 All Forums

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 12:36 PM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.