Go Back   Mike Holt's Forum > Electrical Contracting and Estimating/Management
Forgot Login Information?
Register FAQ About Moderators Members List Calendar Search Today's Posts Mark Forums Read
Reply
Thread Tools Search this Thread Display Modes
  #21
Old 11-05-2009, 10:58 AM
480sparky's Avatar
480sparky 480sparky is online now
Default
Quote:
Originally Posted by A-1Sparky View Post
....... but wouldn't have to have GFI protection. ............
Yes it will.
__________________
Age is just a number but mine is unlisted.
  #22
Old 11-05-2009, 11:20 AM
raider1's Avatar
raider1 raider1 is offline
Default
Quote:
Originally Posted by 480sparky View Post
Yes it will.
If the receptacle is installed more than 12" below the countertop then it can't be counted as the receptacle to serve the countertop, so therefore IMHO it need not be GFCI protected.
Chris
__________________
Facts are meaningless. You could use facts to prove anything that's even remotely true!
  #23
Old 11-05-2009, 11:36 AM
480sparky's Avatar
Default
Quote:
Chris
Silly me..... I have 210.8(B) On The Brain this morning.
__________________
  #24
Old 11-05-2009, 11:41 AM
raider1's Avatar
Default
No problem, it happens to the best of us.
Chris
__________________
  #25
Old 11-05-2009, 07:33 PM
raider1's Avatar
Default
210.8(A)(6) requires that receptacles that are installed to serve the countertop in a dwelling unit kitchen must be GFCI protected.
Now 210.52(C)(5) states that receptacles installed to serve the countertop must be located above the countertop but not more than 20 inches above. The exception to 210.52(C)(5) permits (under specific conditions) the receptacle on an island or peninsular countertop to be located not mor than 12" below the countertop.
So receptacles that don't meet these requirements are not required to be GFCI protected.
Chris
__________________
  #26
Old 11-05-2009, 07:36 PM
pjsullivan pjsullivan is offline
Junior Member
Default
Thanks Chris. Much appreciated.
  #27
Old 11-05-2009, 07:49 PM
raider1's Avatar
Default
Your very welcome.
Chris
__________________
Reply
NEC Ready Forums
Search this Thread:
Advanced Search
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
- Archive - Top
Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.