  #21  
Old 11-05-2009, 09:58 AM
480sparky's Avatar
480sparky 480sparky is online now
Senior Member
 
Join Date: Jul 2007
Location: West of billsnuff
Posts: 14,887
Default

Quote:
Originally Posted by A-1Sparky View Post
....... but wouldn't have to have GFI protection. ............

Yes it will.
__________________
All posts entered between 4:17 and 4:18 AM CDT will be worded to please Bob.
  #22  
Old 11-05-2009, 10:20 AM
raider1's Avatar
raider1 raider1 is offline
Moderator
 
Join Date: Jun 2005
Location: North Logan, Utah
Posts: 6,276
Default

Quote:
Originally Posted by 480sparky View Post
Yes it will.
If the receptacle is installed more than 12" below the countertop then it can't be counted as the receptacle to serve the countertop, so therefore IMHO it need not be GFCI protected.

Chris
__________________
2010 Chief Moderator
  #23  
Old 11-05-2009, 10:36 AM
480sparky's Avatar
480sparky 480sparky is online now
Senior Member
 
Join Date: Jul 2007
Location: West of billsnuff
Posts: 14,887
Default

Quote:
Originally Posted by raider1 View Post
If the receptacle is installed more than 12" below the countertop then it can't be counted as the receptacle to serve the countertop, so therefore IMHO it need not be GFCI protected.

Chris

Silly me..... I have 210.8(B) On The Brain this morning.
__________________
All posts entered between 4:17 and 4:18 AM CDT will be worded to please Bob.
  #24  
Old 11-05-2009, 10:41 AM
raider1's Avatar
raider1 raider1 is offline
Moderator
 
Join Date: Jun 2005
Location: North Logan, Utah
Posts: 6,276
Default

Quote:
Originally Posted by 480sparky View Post
Silly me..... I have 210.8(B) On The Brain this morning.
No problem, it happens to the best of us.

Chris
__________________
2010 Chief Moderator
  #25  
Old 11-05-2009, 06:33 PM
raider1's Avatar
raider1 raider1 is offline
Moderator
 
Join Date: Jun 2005
Location: North Logan, Utah
Posts: 6,276
Default

210.8(A)(6) requires that receptacles that are installed to serve the countertop in a dwelling unit kitchen must be GFCI protected.

Now 210.52(C)(5) states that receptacles installed to serve the countertop must be located above the countertop but not more than 20 inches above. The exception to 210.52(C)(5) permits (under specific conditions) the receptacle on an island or peninsular countertop to be located not mor than 12" below the countertop.

So receptacles that don't meet these requirements are not required to be GFCI protected.

Chris
__________________
2010 Chief Moderator
  #26  
Old 11-05-2009, 06:36 PM
pjsullivan pjsullivan is offline
Junior Member
 
Join Date: Sep 2003
Location: Round Rock, TX
Posts: 12
Default

Thanks Chris. Much appreciated.
  #27  
Old 11-05-2009, 06:49 PM
raider1's Avatar
raider1 raider1 is offline
Moderator
 
Join Date: Jun 2005
Location: North Logan, Utah
Posts: 6,276
Default

Your very welcome.

Chris
__________________
2010 Chief Moderator
Closed Thread

SpecialBanner1 All Forums

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 12:50 PM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.