Go Back   Mike Holt's Forum > Power Quality & Surge Protection
Forgot Login Information?
Register FAQ About Moderators Members List Calendar Search Today's Posts Mark Forums Read

Closed Thread
 
Thread Tools Search this Thread Display Modes
  #11  
Old 11-06-2009, 11:37 AM
S'mise's Avatar
S'mise S'mise is offline
Senior Member
 
Join Date: Jan 2007
Location: Michigan
Posts: 377
Default

The links were very helpful in explaining. So... if a cap is not used to limit inrush (As I was always told) why do they use them on lighting fixtures and similar things? Yes, I realize they are used to help start motors (phase shift)
__________________
John,
  #12  
Old 11-06-2009, 01:59 PM
gar gar is offline
Senior Member
 
Join Date: Apr 2008
Location: Ann Arbor, Michigan
Posts: 2,441
Default

091106-1351 EST

S'mise:

First, about capacitors. If a capacitor has zero initial charge, then its initial voltage is zero. At the instant of connecting a circuit to this capacitor the initial current will be the same as if the capacitor had a short across it. If the source was a 100 V battery and the circuit was a resistor of 1 ohm, then the initial current would be 100 A. Some time in the future that current will drop to zero. In between it follows an exponential curve for the simple RC circuit with a fixed DC source voltage.

Second, what are lighting fixtures and similar things?

.
  #13  
Old 11-07-2009, 08:27 AM
gar gar is offline
Senior Member
 
Join Date: Apr 2008
Location: Ann Arbor, Michigan
Posts: 2,441
Default

091107-0823 EST

S'mise:

Following is a site that you might find informative on a simple RC circuit. There are three pages.

http://www.electronics-tutorials.ws/rc/rc_1.html

.
  #14  
Old 11-07-2009, 03:02 PM
S'mise's Avatar
S'mise S'mise is offline
Senior Member
 
Join Date: Jan 2007
Location: Michigan
Posts: 377
Default Ahh ha!

Thanks Gar, I now see where my logic was flawed. I did remember correctly that Inductive reactance and capacative reactance counteract each other. But, I was confusing inrush and inductive reactance as the same thing. The instances where I have seen caps used with inductive devices were not "used to lessen inrush" (as I was mistakenly told some 20 years ago) but were actually used as a snubber to filter out voltage spikes (noise if you will) after turning off power to these inductive devices. So you were right that a cap would not help inrush current, but they can be used control spikes(outrush current) Thanks for setting me straight.
I love those ah-ha moments where I learn something.
__________________
John,
  #15  
Old 11-07-2009, 03:59 PM
gar gar is offline
Senior Member
 
Join Date: Apr 2008
Location: Ann Arbor, Michigan
Posts: 2,441
Default

091107-1554 EST

S'mise:

Yes the capacitors can help reduce transient spikes on turn-off of an inductive load.

Sometimes these include a series resistor with the capacitor to reduce the time of the transient decay. This is especially useful in a DC circuit, such as an electromechanical clutch, where the desire is to minimize the drop-out time without an excessive peak transient voltage.

.
  #16  
Old 11-07-2009, 08:56 PM
S'mise's Avatar
S'mise S'mise is offline
Senior Member
 
Join Date: Jan 2007
Location: Michigan
Posts: 377
Default

yes, I remember rc circuits from electronics.

As to the op, Sounds like a resistor would be a practical solution to limit inrush current provided that vd would not be a problem.
__________________
John,
  #17  
Old 11-08-2009, 03:15 AM
Besoeker's Avatar
Besoeker Besoeker is offline
Senior Member
 
Join Date: Sep 2008
Location: UK
Posts: 1,901
Default

Quote:
Originally Posted by S'mise View Post
yes, I remember rc circuits from electronics.

As to the op, Sounds like a resistor would be a practical solution to limit inrush current provided that vd would not be a problem.
One technique to reduce inrush is to fit the resistor then short it out after a small delay.
We sometimes do that in our works when we are testing high current low voltage rectifier units where the transformer inrush would exceed the rating of the test outlet being used.
  #18  
Old 11-08-2009, 03:47 PM
S'mise's Avatar
S'mise S'mise is offline
Senior Member
 
Join Date: Jan 2007
Location: Michigan
Posts: 377
Default

Sounds like a standard soft-start ckt.
I have heard of tsr relays that greatly reduce inrush by incorporating thyristors that fire correct polarity, followed by relay shunting the ckt closed.
Very clever stuff but they sound expensive.
__________________
John,
  #19  
Old 11-09-2009, 06:33 AM
Besoeker's Avatar
Besoeker Besoeker is offline
Senior Member
 
Join Date: Sep 2008
Location: UK
Posts: 1,901
Default

Quote:
Originally Posted by S'mise View Post
Sounds like a standard soft-start ckt.
I have heard of tsr relays that greatly reduce inrush by incorporating thyristors that fire correct polarity, followed by relay shunting the ckt closed.
Very clever stuff but they sound expensive.
Using a resistor to limit inrush current isn't like a soft start circuit.
The resistor is just two discrete stages. It's in circuit or shorted.
By contrast, the thyristor soft start provides a continuously variable voltage.
Clever and expensive? I wouldn't have thought so.
Simple light dimmers can use either triacs at the low power end or thyristors at higher powers. It's fairly well-established technology. Light dimmers are not generally very expensive.
  #20  
Old 11-09-2009, 09:24 AM
gar gar is offline
Senior Member
 
Join Date: Apr 2008
Location: Ann Arbor, Michigan
Posts: 2,441
Default

091109-0915 EST

To limit transformer inrush current that results from core saturation there is no valid reason to use a phase shift controlled device. A resistor will do the job. This inrush is largely a 1/2 cycle effect as shown in my previously mentioned photos. Keeping a suitable resistor in series with the transformer primary for several cycles is more than adequate to reduce the inrush problem.

.
Closed Thread

SpecialBanner1 All Forums

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 12:41 PM.