Fight this all the way...the neutral does not have to be carried past the service if it is not needed downstream...
Feeders and Branch Circuits are generally not taps. |
|
#12
|
|||
|
|||
|
Quote:
|
|
#13
|
|||
|
|||
|
Quote:
__________________
Cheers and Stay Safe, Marky the Sparky OSHA 1910.304(g)(2)(iv) "One phase conductor of a multiphase system where one phase is grounded shall be grounded" |
|
#14
|
|||
|
|||
|
No, grounding conductors are not brought in with the service conductors, they are only
run after the first service disconnecting means. It is at this disconnecting means that the " grounded service conductor " and the EGC's are tied together. If the grounded conductor was not brought in with the service conductors, there would be no path for the EGC's to carry the fault current to and trip the c.b.
__________________
Frank Arizona,USA |
|
#15
|
|||
|
|||
|
If you are havng a beef with an AHJ that's important to resolve in your favor, get an informal technical interpretation from the NEC. Go to the NEC website and look under member services and it explains the process. You can do it by phone or email, and an informal interpretation is generally mighty quick. It's an awesome member benefit. The AHJ can still think whatever they want because they are the AHJ, but in my experience people don't want to be hanging out there on their own without NFPA cover.
|
|
#16
|
|||
|
|||
|
Another way to look at this is: Is the AHJ above and beyond the law? Would his argument stand up in a court of law? Will you suffer damages by delay or by having to put an unused conductor into your conduits? And lastly, is there an engineering stamp on the set of drawings your project is concerned with ? It would behoove the engineer to solve this problem for you if there is such a drawing submitted with his stamp.
__________________
85deg. an Sunny today. |
|
#17
|
|||
|
|||
|
His terminology was correct.
|
|
#18
|
||||
|
||||
|
Not in my opinion. I believe the NEC (and/or other adopted code) is as binding on the inspector as it is on the contractor.
I believe it's as illegal to fail something incorrectly as it is to pass something incorrectly, just as with vehicle inspections.
__________________
Code references based on 2005 NEC Larry B. FineElectrical Contractor Richmond, VA |
|
#19
|
|||
|
|||
|
Take his article 200 and give him article 100, Premises Wiring
|
|
#20
|
||||
|
||||
|
Talking to someone who is normally "in the know"said try leading the horse down this trail -
The answer lies in the text of 200.2. This section requires premise wiring systems to have a grounded conductor. A single branch circuit or feeder is not by itself a system.
__________________
Don't let fear be your guide! |
![]() |