Quote:
Originally Posted by winnie View Post
At full load current, the voltage across the transformers internal impedance is essentially what you expect from the % impedance _However_, the voltage across the internal impedance will likely be at a different phase angle than the load voltage, so you need to use vector math to determine the voltage drop actually seen by the load.

The transformer impedance has a fairly low inductive power factor. The most loads have a slightly inductive high power factor. The voltage drop seen by such a load will be a fraction of the voltage across the transformer impedance.

If the load has a poor inductive power factor, then it will see greater voltage drop; if the load has a significant capacitive power factor, it can even see its voltage _rise_.

-Jon
That makes everything a lot clearer. Thanks.
Steve
  #12  
Old 11-09-2009, 04:14 PM
steve66 steve66 is offline
Senior Member
 
Join Date: Jun 2003
Posts: 4,374
Default

Quote:
Originally Posted by Besoeker View Post
Yes. Voltage regulation and impedance are two different things.
I have a spreadsheet I use for estimating voltage drop*.

I took the model and loaded the transformer (Z at 5%) to its full current rating for different PF loads.
At 0.8 lag, the voltage drop is 3.9%. At unity pf it is 1.34%.

*I'm an indolent old fellow. If I do the mathematics once and put it in a form where I can make use of it again it saves me time and effort.
With SKM software, I also get about 3.9% at 0.8 lag.

But for unity, I get about 1.1%. If I give the xformer a very high X/R ratio, that drops to almost 0%.

For very low PF loads, the voltage drop is close to the %Z. For a PF =0.5, the voltage drop is very close to 5%. For a PF = 0, the voltage drop is just a little higher at about 5.3%.

So it seems like it would be pretty safe to assume the voltage drop is normally going to be something ess than the %Z.

Steve
  #13  
Old 11-11-2009, 02:22 PM
mivey's Avatar
mivey mivey is offline
Senior Member
 
Join Date: Jan 2008
Posts: 4,763
Default Formulas

Z^2 = R^2 + X^2 for percent impedance, resistance & reactance

R = load loss / 10 / kVA

% voltage regulation = sqrt[R^2 + X^2 + 200 x (Xsin@ + Rcos@) + 10000] - 100
where @ is the power factor angle (+ for inductive) and impedance components are in %.

ex. 37.5 kVA 7200/12470Y-120/240 with no-load loss of 155, rated loss = 568, 1.86% impedance:

R = (568-155) / 10 / 37.5 = 1.1%
X = sqrt(1.86^2 - 1.1^2) = 1.5%

For 50% p.f.:
Reg = sqrt[1.1^2 + 1.5^2 + 200 x (1.5 x 0.866 + 1.1 x 0.50) + 10000] - 100 = 1.849%

For 80% p.f.:
Reg = sqrt[1.1^2 + 1.5^2 + 200 x (1.5 x 0.6 + 1.1 x 0.80) + 10000] - 100 = 1.781%

For unity p.f.:
Reg = sqrt[1.1^2 + 1.5^2 + 200 x (1.5 x 0 + 1.1 x 1.0) + 10000] - 100 = 1.111%
__________________
BB+/BB=?
  #14  
Old 11-11-2009, 05:48 PM
bob's Avatar
bob bob is online now
Senior Member
 
Join Date: Feb 2003
Location: Nashville
Posts: 2,063
Default

% voltage regulation = sqrt[R^2 + X^2 + 200 x (Xsin@ + Rcos@) + 10000] - 100
where @ is the power factor angle (+ for inductive) and impedance components are in %.


Miley
I am not following this formula. What are the 200, 10000 and 100?
  #15  
Old 11-11-2009, 06:11 PM
mivey's Avatar
mivey mivey is offline
Senior Member
 
Join Date: Jan 2008
Posts: 4,763
Default

Quote:
Originally Posted by bob View Post
% voltage regulation = sqrt[R^2 + X^2 + 200 x (Xsin@ + Rcos@) + 10000] - 100
where @ is the power factor angle (+ for inductive) and impedance components are in %.

Miley
I am not following this formula. What are the 200, 10000 and 100?
I did not derive the formula as it came out of a transformer handbook.
__________________
BB+/BB=?
  #16  
Old 11-11-2009, 06:17 PM
Cold Fusion Cold Fusion is offline
Senior Member
 
Join Date: Jul 2008
Location: way north
Posts: 1,260
Default

Quote:
Originally Posted by mivey View Post
...R = load loss / 10 / kVA ...
And I need help figuring where this one comes from. Is this an assumption that the X/R ratio is 10.

cf
__________________
I deal with the laws of God and physics, the laws of man are a sorry second.
  #17  
Old 11-11-2009, 06:25 PM
mivey's Avatar
mivey mivey is offline
Senior Member
 
Join Date: Jan 2008
Posts: 4,763
Default

Quote:
Originally Posted by Cold Fusion View Post
And I need help figuring where this one comes from. Is this an assumption that the X/R ratio is 10.

cf
No. It is the conversion between watts, kVA and percent. The loss was in watts and the transformer size in kVA and R in %.
__________________
BB+/BB=?
  #18  
Old 11-12-2009, 12:59 AM
Cold Fusion Cold Fusion is offline
Senior Member
 
Join Date: Jul 2008
Location: way north
Posts: 1,260
Default

Quote:
Originally Posted by mivey View Post
No. It is the conversion between watts, kVA and percent. The loss was in watts and the transformer size in kVA and R in %.
Ahhh - thank you

cf
__________________
I deal with the laws of God and physics, the laws of man are a sorry second.
  #19  
Old 11-12-2009, 01:48 PM
Besoeker's Avatar
Besoeker Besoeker is offline
Senior Member
 
Join Date: Sep 2008
Location: UK
Posts: 1,901
Default

Quote:
Originally Posted by steve66 View Post
With SKM software, I also get about 3.9% at 0.8 lag.

But for unity, I get about 1.1%.
I used an X/R ratio that is typical for many of the power transformers we use.
It's also that which use for calculating system losses.
I don't think we can fall out over a difference of about 0.2%.
Closed Thread

CEU Banner Forum Pages

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 12:39 PM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.