314.24(C) differentiates between outlet boxes and device boxes.

314.27 no mention of switches.

Does the box that the LED luminaire was installed in, have a mark on the interior to indicate the maximum weight of the luminaire that is permitted to be supported by the lighting outlet box?
  #62  
Old 11-06-2009, 02:35 PM
al hildenbrand's Avatar
al hildenbrand al hildenbrand is offline
Senior Member
 
Join Date: Feb 2003
Location: Minnesota
Posts: 3,872
Default

Quote:
Originally Posted by wasasparky View Post
314.24(C) differentiates between outlet boxes and device boxes.
The phrase "Outlet and device . . ." is used repeatedly while 314.24 describes minimum internal depth of the enclosure. I don't see that it describes the differences (differentiation) between Outlets and Devices.
Quote:
Originally Posted by wasasparky View Post
314.27 no mention of switches.

Does the box that the LED luminaire was installed in, have a mark on the interior to indicate the maximum weight of the luminaire that is permitted to be supported by the lighting outlet box?
Don't overlook the exception to 314.27(A)
Quote:
2008 NEC
314.27(A) Exception: A wall-mounted luminaire weighing not more than 3 kg (6 lb) shall be permitted to be supported on other boxes or plaster rings that are secured to other boxes, provided the luminaire or its supporting yoke is secured to the box with no fewer than two No. 6 or larger screws.
__________________
Another Al in Minnesota
  #63  
Old 11-06-2009, 03:04 PM
LarryFine's Avatar
LarryFine LarryFine is offline
Senior Member
 
Join Date: May 2005
Location: Richmond, Virginia
Posts: 19,881
Default

Quote:
Originally Posted by al hildenbrand View Post


The luminaire yoke, the plastic luminaire body and the one label (see photo above) have absolutely no electrical info other than "20A per circuit. 15A each. 120VAC"
But, it does say "luminaire" right in the middle.
__________________
Code references based on 2005 NEC
Larry B. Fine
Master Electrician
Electrical Contractor
Richmond, VA
  #64  
Old 11-06-2009, 07:13 PM
al hildenbrand's Avatar
al hildenbrand al hildenbrand is offline
Senior Member
 
Join Date: Feb 2003
Location: Minnesota
Posts: 3,872
Default

Quote:
Originally Posted by LarryFine View Post
But, it does say "luminaire" right in the middle.
Sorry. I should have tied that statement a little tighter to the load information that I was hoping to find.
__________________
Another Al in Minnesota
  #65  
Old 11-08-2009, 10:41 PM
cschmid's Avatar
cschmid cschmid is offline
Senior Member
 
Join Date: Aug 2003
Location: Northern cold country
Posts: 2,611
Default

I have installed a bunch of these and like them and so does everyone I know who has them installed..You raised an interesting debate. I wonder what the debate was like before this was marketed???
__________________
Life is temporary, heaven is forever. live life like it is your only chance to make a difference..

to do nothing is the surest way to achieve nothing..
  #66  
Old 11-08-2009, 11:59 PM
al hildenbrand's Avatar
al hildenbrand al hildenbrand is offline
Senior Member
 
Join Date: Feb 2003
Location: Minnesota
Posts: 3,872
Default

Quote:
Originally Posted by cschmid View Post
I wonder what the debate was like before this was marketed???
I have two thoughts.

One is tied to the White Book classification of this LED luminaire as an incandescent luminaire. I've worked in a large number of 1890 thru 1920 single family dwellings. They commonly, but not always, had evidence of a switch controlled receptacle in the kitchen. The switch and the single receptacle, each in their own yokes, were under a three gang coverplate.

The central gang, of the three gang plate, was a jewel lensed incandescent indicator light. The most common bulb was the venerable C7 Christmas decoration type.

Turning the switch on energized both the indicator light and the receptacle.

I suspect the White Book classification of the LED luminaire is this same device carried forward in time.

Until the advent of the AFCI and 210.12(B) I doubt that hardly anyone gave a yoke mounted luminaire much thought at all. Maybe there was a debate about whether the luminaire was Utilization Equipment, or not. . . but that boils down to what an Outlet is.

As long as part of the 15 and 20 Amp 125 Volt branch circuits in a Dwelling are not AFCI protected there will be a need to understand what an Outlet is, IMO.
__________________
Another Al in Minnesota
  #67  
Old 11-09-2009, 12:42 AM
flashlight flashlight is offline
Senior Member
 
Join Date: Jun 2006
Location: NY, NY
Posts: 222
Default

Quote:
Originally Posted by drbond24 View Post
That definition came from the NEC.......The requirements they call out are a light source, positioning, and power supply connection. All are present in this case.
Is a porcelain lamp holder a luminaire ? I remember reading here that it isn't, but it seems to have these 3 elements.
  #68  
Old 11-09-2009, 08:39 AM
wasasparky wasasparky is offline
Senior Member
 
Join Date: May 2006
Posts: 293
Default

Quote:
Originally Posted by al hildenbrand View Post
...provided the luminaire or its supporting yoke is secured to the box with no fewer than two No. 6 or larger screws.
What size are the screws in the LED luminaire?
  #69  
Old 11-09-2009, 10:25 AM
al hildenbrand's Avatar
al hildenbrand al hildenbrand is offline
Senior Member
 
Join Date: Feb 2003
Location: Minnesota
Posts: 3,872
Default

Quote:
Originally Posted by wasasparky View Post
What size are the screws in the LED luminaire?


This P&S TMHWL hallway luminaire has two standard #6-32 device screws.
__________________
Another Al in Minnesota
  #70  
Old 11-13-2009, 10:48 PM
cschmid's Avatar
cschmid cschmid is offline
Senior Member
 
Join Date: Aug 2003
Location: Northern cold country
Posts: 2,611
Default

I have not seen one of the receptacles you discribe in years and I suppose the idea may of stemmed from the use of the indicator light receptacle. I would think the amperage of the night light receptacle is less then the 1.8 allowed per receptacle in the calculation. I believe this is one of the most useful inventions in a long time.

Now I have not researched this as my computer crashed thanks to some Qwest software and the lack of proper directions. apparently I needed to due some clean up on my laptop and now it is deer hunting. So next week when I am hanging around the home away from I will check it out.
__________________
Life is temporary, heaven is forever. live life like it is your only chance to make a difference..

to do nothing is the surest way to achieve nothing..
Closed Thread

SpecialBanner1 All Forums

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 12:39 PM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.