Does your residential ground wire have to be a continous run of wire?
Are you asking about the GEC or an EGC?
Roger
The grounding electrode conductor (GEC) per 250.64 (C) (1) 2014 NEC
allows splices but the splice must be irreversible compression connectors listed for grounding and bonding or by exothermic welding.