mshields

Senior Member
Location
Boston, MA
I'm designing how to bring power to a series of heated panels on the intake of an AHU; it's a snowmelt system. Each panel has a screw in terminal with a whip to which I'm going to connect a fitting for converting to a flxible cord. The flexible cord will have a NEMA 5-20L twist lock plug on it and of course go to a nearby NEMA 5-20L receptacle in a weather proof enclosure.

My question is what should I specify for the cable. It will be completely exposed to the elements all winter long.

Thank you,

Mike
 

mwm1752

Senior Member
Location
Aspen, Colo
Reconfiguring or not following installation instructions of a listed unit will make it a non compliant installation. or Are you trying to design something for a NRTL to list? The NEC has a table on cords & applications for you to determine which is best.
 

mshields

Senior Member
Location
Boston, MA
SOOW looks good

SOOW looks good

good down to -40C/F (they are the same at that degree - I didn't know that). In any event it doesn't get THAT cold up here.

Thanks,

Mike
 