#31
|
||||
|
||||
|
Quote:
Can anyone show me where this can not be accomplished by use of the grounding conductor of the circuit??
__________________
"America will never be destroyed from the outside. If we falter and lose our freedoms, it will be because we destroyed ourselves." Abraham Lincoln |
|
#32
|
||||
|
||||
|
I think it could be argued that section 250.104(c) applies to exposed structural metal as described whether or not there is even a branch circuit run to the building .
__________________
"America will never be destroyed from the outside. If we falter and lose our freedoms, it will be because we destroyed ourselves." Abraham Lincoln |
|
#33
|
|||
|
|||
|
M.D.,
What do you think of 250.32(B)(1), IMO, it covers this aspect.
__________________
Frank Arizona,USA It's what you learn after you know it all that counts !! |
|
#34
|
||||
|
||||
|
Quote:
__________________
"America will never be destroyed from the outside. If we falter and lose our freedoms, it will be because we destroyed ourselves." Abraham Lincoln |
|
#35
|
||||
|
||||
|
Dennis
The equipment ground conductor installed with the supply conductors (12/3) is sufficiently sized. Why 250.66 keeps being discussed I am not sure. 250.104(A)(3) Multiple Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s). The bonding jumper shall not be required to be larger than the largest ungrounded feeder or branch circuit conductor supplying the building. This is the last sentence of the subsection. If you are supplying wiring to the metal structure, the question is not will it become energized, the comment is I do not know if it will ever become energized. That is good enough to say it the bonding is necessary, as in our industry we try not to leave any safety aspect in question. If at worst, use a short bonding jumper connected to the box and the steel structure as your required bonding jumper. Then you are done .
__________________
Instructor, Industry Advocate |
|
#36
|
||||
|
||||
|
Quote:
250.104(c) requires his frame to be ,.. and 250.32 says the EGC can be
__________________
"America will never be destroyed from the outside. If we falter and lose our freedoms, it will be because we destroyed ourselves." Abraham Lincoln |
|
#37
|
||||
|
||||
|
Quote:
Under normal conditions the building is likely NOT to become energized. If the wording was "likely to become energized under xyz conditions" or "in the event of whatever" it might have more weight as far as an absolute requirement for bonding. In my view anyway.
__________________
There are two kinds of people - those smart enough to know they don’t know, and those dumb enough to insist they do.-----Margery Eagan |
|
#38
|
||||
|
||||
|
Two definitions ,.. niether of which are found in the NEC so take them for what they are I guess,... a couple more opinions
Quote:
Quote:
__________________
"America will never be destroyed from the outside. If we falter and lose our freedoms, it will be because we destroyed ourselves." Abraham Lincoln |
|
#39
|
||||
|
||||
|
Quote:
![]() I guess the NEC just ignores the actual definitons of words and substitutes what they want something to mean.
__________________
There are two kinds of people - those smart enough to know they don’t know, and those dumb enough to insist they do.-----Margery Eagan |
|
#40
|
||||
|
||||
|
Well I called the nc state inspector because I was curious as to his interpretation. He absolutely agrees that the #4 bond is unnecessary and that the EGC of the circuit is all that is needed because it is a separate structure. I guess the rules change if this was an attached structure.
__________________
The National Sarcasm Society Like We Really Need Your Support |
![]() |