Quote:
Originally Posted by raider1 View Post
.........

According to 250.104(C) I must size the bonding conductor in accordance with 250.66 and install the conductor like a GEC.

Chris
Only if the exposed structural metal has not been intetionally grounded .. once you satisfy this,. the rest is moot.

Can anyone show me where this can not be accomplished by use of the grounding conductor of the circuit??
__________________
"America will never be destroyed from the outside.
If we falter and lose our freedoms,
it will be because we destroyed ourselves."

Abraham Lincoln
  #32  
Old 11-06-2009, 06:59 AM
M. D.'s Avatar
M. D. M. D. is offline
Senior Member
 
Join Date: Mar 2006
Posts: 3,852
Default

Quote:
Originally Posted by benaround View Post
Dennis,

I really don't see any other section that pertains to your situation except for 250.32, Its'
I think it could be argued that section 250.104(c) applies to exposed structural metal as described whether or not there is even a branch circuit run to the building .
__________________
"America will never be destroyed from the outside.
If we falter and lose our freedoms,
it will be because we destroyed ourselves."

Abraham Lincoln
  #33  
Old 11-06-2009, 07:16 AM
benaround benaround is offline
Senior Member
 
Join Date: Mar 2004
Location: Arizona
Posts: 3,909
Default

M.D.,

What do you think of 250.32(B)(1), IMO, it covers this aspect.
__________________
Frank Arizona,USA
  #34  
Old 11-06-2009, 07:41 AM
M. D.'s Avatar
M. D. M. D. is offline
Senior Member
 
Join Date: Mar 2006
Posts: 3,852
Default

Quote:
Originally Posted by benaround View Post
M.D.,

What do you think of 250.32(B)(1), IMO, it covers this aspect.
I'd say I agree 250.32 (b) covers his situation.
__________________
"America will never be destroyed from the outside.
If we falter and lose our freedoms,
it will be because we destroyed ourselves."

Abraham Lincoln
  #35  
Old 11-06-2009, 07:56 AM
Pierre C Belarge's Avatar
Pierre C Belarge Pierre C Belarge is offline
Senior Member
 
Join Date: Mar 2006
Location: Westchester County, New York
Posts: 7,791
Default

Dennis
The equipment ground conductor installed with the supply conductors (12/3) is sufficiently sized.
Why 250.66 keeps being discussed I am not sure.


250.104(A)(3) Multiple Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s).

The bonding jumper shall not be required to be larger than the largest ungrounded feeder or branch circuit conductor supplying the building.



This is the last sentence of the subsection.



If you are supplying wiring to the metal structure, the question is not will it become energized, the comment is I do not know if it will ever become energized. That is good enough to say it the bonding is necessary, as in our industry we try not to leave any safety aspect in question.


If at worst, use a short bonding jumper connected to the box and the steel structure as your required bonding jumper. Then you are done .
__________________
Instructor, Industry Advocate
  #36  
Old 11-06-2009, 08:03 AM
M. D.'s Avatar
M. D. M. D. is offline
Senior Member
 
Join Date: Mar 2006
Posts: 3,852
Default

Quote:
Originally Posted by Pierre C Belarge View Post
Dennis
The equipment ground conductor installed with the supply conductors (12/3) is sufficiently sized.
Why 250.66 keeps being discussed I am not sure.


250.104(A)(3) Multiple Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s).

The bonding jumper shall not be required to be larger than the largest ungrounded feeder or branch circuit conductor supplying the building.



This is the last sentence of the subsection.
Yah,.. only that section deals with bonding metal water piping systems.


250.104(c) requires his frame to be ,.. and 250.32 says the EGC can be
__________________
"America will never be destroyed from the outside.
If we falter and lose our freedoms,
it will be because we destroyed ourselves."

Abraham Lincoln
  #37  
Old 11-06-2009, 07:14 PM
electricmanscott's Avatar
electricmanscott electricmanscott is offline
Senior Member
 
Join Date: Feb 2003
Location: I Live in Holden Massachusetts, if you're in the area, look me up
Posts: 6,588
Default

Quote:
Originally Posted by Pierre C Belarge View Post
Dennis


If you are supplying wiring to the metal structure, the question is not will it become energized, the comment is I do not know if it will ever become energized. That is good enough to say it the bonding is necessary, as in our industry we try not to leave any safety aspect in question.
I don't really agree. The NEC says "likely to become energized" . To me saying I don't know if it will become energized is allot different than saying it is likely to become energized.

Under normal conditions the building is likely NOT to become energized.

If the wording was "likely to become energized under xyz conditions" or "in the event of whatever" it might have more weight as far as an absolute requirement for bonding. In my view anyway.
__________________
There are two kinds of people - those smart enough to know they don’t know, and those dumb enough to insist they do.-----Margery Eagan

Open shop since 1988
  #38  
Old 11-06-2009, 08:00 PM
M. D.'s Avatar
M. D. M. D. is offline
Senior Member
 
Join Date: Mar 2006
Posts: 3,852
Default

Two definitions ,.. niether of which are found in the NEC so take them for what they are I guess,... a couple more opinions

Quote:
The NEC style manual

Likely to Become Energized: Failure of insulation on


Quote:
by Jeffrey Sargent, Noel Williams
Likely to Become Energized:
Failure of insulation on energized parts or conductors........
..........likely in this sense does not address the probability that an insulation failure will occur.
__________________
"America will never be destroyed from the outside.
If we falter and lose our freedoms,
it will be because we destroyed ourselves."

Abraham Lincoln
  #39  
Old 11-07-2009, 05:45 AM
electricmanscott's Avatar
electricmanscott electricmanscott is offline
Senior Member
 
Join Date: Feb 2003
Location: I Live in Holden Massachusetts, if you're in the area, look me up
Posts: 6,588
Default

Quote:
Originally Posted by M. D. View Post
Two definitions ,.. niether of which are found in the NEC so take them for what they are I guess,... a couple more opinions
Those are great.

I guess the NEC just ignores the actual definitons of words and substitutes what they want something to mean.
__________________
There are two kinds of people - those smart enough to know they don’t know, and those dumb enough to insist they do.-----Margery Eagan

Open shop since 1988
  #40  
Old 11-07-2009, 07:18 AM
Dennis Alwon's Avatar
Dennis Alwon Dennis Alwon is online now
Senior Member
 
Join Date: Dec 2006
Location: Chapel Hill, NC
Posts: 13,847
Default

Well I called the nc state inspector because I was curious as to his interpretation. He absolutely agrees that the #4 bond is unnecessary and that the EGC of the circuit is all that is needed because it is a separate structure. I guess the rules change if this was an attached structure.
__________________
4 Out Of 3 People Have Trouble With Fractions

The National Sarcasm Society
Like We Really Need Your Support
Closed Thread

CEU Banner Forum Pages

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 12:17 PM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.