Does the disconnect for the main elevator supply need to be fused in the machine control room
Does the disconnect for the main elevator supply need to be fused in the machine control room
Yes 620.51(A) and within in sight of the controller. I see you are looking at 620.51(C)(1) and (2)
Yes you need a shunt trip breaker or a relay. So as when the sprinlkers come on above the elevator eqipment. The elevator will stop, hope fully on a floor:wink:
But is it saying that I "Must" do this??? It says "shall be permitted". To me that sounds like I have a choice. Am I just reading this wrong. What do you other guys know or say?
Yes you need a shunt trip breaker or a relay. So as when the sprinlkers come on above the elevator equipment. The elevator will stop, hope fully on a floor:wink:
I'm trying to get finished with a job. It's an all hydraulic elevator there's no sprinkler head above the cab,
there's only one sprinkler in the Pit at 2'-0" off of elevation of the pit floor. ((AS I RECALL))
The elevator today passed the recall by interface with the F/A, the shunt trip breaker preformed well also!
The engineer of record missed it in their design!
I beleive its a Dept of Labor / via the Dept of Insurance requirement in our state.
Welcome to the Forum - Local ...
Was your shunt trip located remote from the machine room and you had a fused disconnect in the machine room?
Was your shunt trip located remote from the machine room and you had a fused disconnect in the machine room?
Does the disconnect for the main elevator supply need to be fused in the machine control room
620.51 (A) of the 2005 codes says the disconnecting means shall be a fused motor switch or a circuit breaker.