Thermal temperatures

Status
Not open for further replies.

CCDTHOMAS

Member
Part of our PM is to do thermal temperatures at the tombstone of flourscent lighting, is there a formula or a spec sheet that would give me the temperature that the lamps at the tombstones should not exceed? I have simple 2 lamp 32 watt instant start ballast.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I guess nobody knows, but I just can't resist anymore.

Isn't "Thermal temperatures" redundant? ;)
 

Volta

Senior Member
Location
Columbus, Ohio
Part of our PM is to do thermal temperatures at the tombstone of flourscent lighting, is there a formula or a spec sheet that would give me the temperature that the lamps at the tombstones should not exceed? I have simple 2 lamp 32 watt instant start ballast.

I don't know of any, but if you start your own log of different lamp and ballast types and the temperatures, let us know what you find!

And watch out for Larry, he might get redundant again :grin:.
 

480sparky

Senior Member
Location
Iowegia
Start taking readings. Once you find a bunch of them with roughly the same temp, then that's your normal operating range.
 