Automatic transfer switch

Status
Not open for further replies.

Big Guns

Member
Is there a code stating the minimum height a NEMA 3R ATS switch could or should be installed on an exterior of a building if so what article. Thank You
 

Smart $

Esteemed Member
Location
Ohio
Depends on whether or not it has a manually operable switch or circuit breaker...

404.8 Accessibility and Grouping.
(A) Location. All switches and circuit breakers used as
switches shall be located so that they may be operated from
a readily accessible place. They shall be installed such that
the center of the grip of the operating handle of the switch
or circuit breaker, when in its highest position, is not more
than 2.0 m (6 ft 7 in.) above the floor or working platform.
Exception No. 1: On busway installations, fused switches
and circuit breakers shall be permitted to be located at the
same level as the busway. Suitable means shall be provided
to operate the handle of the device from the floor.
Exception No. 2: Switches and circuit breakers installed
adjacent to motors, appliances, or other equipment that
they supply shall be permitted to be located higher than 2.0 m
(6 ft 7 in.) and to be accessible by portable means.
Exception No. 3: Hookstick operable isolating switches
shall be permitted at greater heights.

...and even though it may be an ATS, if it has a manual override, I believe it qualifies for the section quoted above.
 