nothing is there just panel is in niche.
Inspector says that is a violation.
Could the violation be the distance back from the wall face, I would say the panel is set back further than 6".
It is definitely a violation. If the recess could be modified to be at least 30" wide and 78" tall (from floor to top of recess) and panel door can open to 90 degrees you will be in compliance.
You cannot have any set back to building finish.
The 6" allowance is only for other electrical equipment.
How many times have I said that? At least most of the time it's been true.And yes we will eat that.
Never happen to me again
Just out of curiosity, why is the wall that deep?Thank you for your help.
And yes we will eat that.
Never happen to me again
Thank you for your help.
And yes we will eat that.
Never happen to me again
How many times have I said that? At least most of the time it's been true.
Just out of curiosity, why is the wall that deep?
Is it an oddball construction like log or straw bale? Or just a very thick wall cavity for insulation purposes?