Pull box size?

Status
Not open for further replies.
I have a run about 120' of 1 1/4" EMT containing four #3 AWG and one #8 AWG to a new sub panel. I need a pull box about mid way. Based 314.28 (A) (1) for a straight pull (1 1/4" x 8 = 10") I need a 10" long box if the conduit comes in one side and exits the opposite end. Can I use a standard conduit C instead of a box?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Only if they are marked to accept you conductors {see 314.28(A)(3)}
(sounds like a good application for a 2-1/2 x 2-1/2 x 12" wireway.)
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I do not understand. :confused:
This has front flanges:
wire_way_Ladder_cable_tray_cable_ladder.jpg




This does not:
3fa36d89112889700cd20c0ddcb0e1d6.jpg

I'm thinking about insulation damage during installation.
 