Meter Points

Status
Not open for further replies.

Canton

Senior Member
Location
Virginia
Occupation
Electrician

I have installed the quadlogics before. You have 3 ct's for each metered point (A,B and C Phase). Most of the mini closets come with either 6 or 8 metered points (18 or 24 ct connections). What exactly are you trying to figure out?

The 3,6,9 and 12 metered points is for a single phase application on a 120/208 service where you are only monitoring two phases. So you would have a ct on only two phases of the metered points (2 phases are being monitored instead of three). Each set makes a metered point.
 
Last edited:

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
So there are places in the country where there is no physical meter per tenant and just one of these boxes.
 

Canton

Senior Member
Location
Virginia
Occupation
Electrician
So there are places in the country where there is no physical meter per tenant and just one of these boxes.

Yes, these are for a sub-metering application. I have usually installed these in commercial applications, tenant spaces, and metering of independent equipment.
 