Default Fire Rating Conductors / Conduit

When installed in conduit (standard building wire thhn thwn in EMT RGS) does the conduit help to provide a "fire rating" for the cables. for example would conductors installed in emt be considered 1hr rated as opposed to rigid that would provide a 2hr rating. is there a table or information on this? without using special fire rated cabling or encased in concrete?
  #2  
Old 11-04-2009, 07:23 PM
ron's Avatar
ron ron is offline
Senior Member
 
Join Date: Feb 2003
Posts: 2,423
Default

No fire rating for regular building wire in conduit.
There is wire in EMT that will get you a fire rating, such as http://www.drakausa.com/productDetai...?productID=732
__________________
Ron
  #3  
Old 11-04-2009, 11:17 PM
sparkie001 sparkie001 is offline
Senior Member
 
Join Date: Sep 2003
Posts: 324
Default

Metallic conduit readily conducts the heat and melts normal wire insulation. Use your favorite search engine and search for ceramified silicone insulated wire which can be installed in EMT and achieve a 2hr rating.
  #4  
Old 11-05-2009, 01:06 AM
Pierre C Belarge's Avatar
Pierre C Belarge Pierre C Belarge is offline
Senior Member
 
Join Date: Mar 2006
Location: Westchester County, New York
Posts: 7,791
Default

Quote:
Originally Posted by ron View Post
No fire rating for regular building wire in conduit.
There is wire in EMT that will get you a fire rating, such as http://www.drakausa.com/productDetai...?productID=732

One item to remember with this type of rated conductor is the cost. There is a dramatic difference in the cost of the above conductor, make sure to price it properly, otherwise you will wish you never took the job.

Read the installation instructions as well, not all phases of this installation are as straight forward as Type THHN installations.
__________________
Instructor, Industry Advocate
  #5  
Old 11-05-2009, 09:55 AM
lakee911 lakee911 is offline
Senior Member
 
Join Date: Jan 2008
Location: Columbus, OH
Posts: 236
Default

Can't you also put standard wire in 2" of concrete to meet fire rating?

Jason
  #6  
Old 11-05-2009, 08:50 PM
don_resqcapt19's Avatar
don_resqcapt19 don_resqcapt19 is offline
Moderator
 
Join Date: Feb 2003
Location: Illinois
Posts: 13,312
Default

The concrete would protect the building from the wires in the conduit, but it will not protect the wires from the fire in the building. Two inches of concrete does not provide much thermal insulation from the heat of a building fire.
__________________
Don, Illinois
"It is the first responsibility of every citizen to question authority." B Franklin
  #7  
Old 11-05-2009, 10:13 PM
sparkie001 sparkie001 is offline
Senior Member
 
Join Date: Sep 2003
Posts: 324
Default

Actually 2 inches of concrete is OK. NEC 695.6 (B) (1)
  #8  
Old 11-06-2009, 11:40 AM
don_resqcapt19's Avatar
don_resqcapt19 don_resqcapt19 is offline
Moderator
 
Join Date: Feb 2003
Location: Illinois
Posts: 13,312
Default

Quote:
Originally Posted by sparkie001 View Post
Actually 2 inches of concrete is OK. NEC 695.6 (B) (1)
I see the code pemits the use of the concrete to protectect the conductors, but I really don't believe the circuit would still be functional, if you use standard wire and 2" of concrete, after exposure to a typical building fire for an hour or so.
__________________
Don, Illinois
"It is the first responsibility of every citizen to question authority." B Franklin
  #9  
Old 11-06-2009, 12:19 PM
Mike01's Avatar
Mike01 Mike01 is offline
Senior Member
 
Join Date: Mar 2007
Location: Michigan
Posts: 542
Default 2hr Cable

After doing some research it turns out the cable is fire rated (1hr, 2hr, 3hr) etc. if is a special fire rated cable complying with the applicable UL standards this includes MI cable, RHW-fire rated cable, and a special MC fire rated cable, however to achieve the 2hr fire rating for the special RHW it has to be installed in conduit and per the manufacturers UL system number the way it was tested. it turns out that 2" concrete encasement is acceptable but the funny thing is that when UL does the test it tests the concrete not the cables the test is carried out without conductors installed in the pipe. interesting. but it turns out you have to use a cable listed to UL standard for the rating you are achieving and install it to the manufacturers UL System number, unless installed in a "fire rated enclosure" built to the UL standard.
Closed Thread

CEU Banner Forum Pages

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 12:42 PM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.