#1
|
|||
|
|||
|
When installing a HRG to a 3-phase 4-wire wye transformer (existing transformer) would it be correct to say that the system is not a solidily grounded system, thereby requiring the existing grounded conductors be removed?
Rick
__________________
If I can't fix it, it's not broke. |
|
#2
|
|||
|
|||
|
Quote:
An HRG can supply a delta primary of a transformer. The wye secondary is a separately derived system which can be solidly grounded and supply L-N loads, it does not impact the primary side HRG.
__________________
I think I have already told you more than I know. |
|
#3
|
||||
|
||||
|
You likely will need to move the grounded conductors to the correct side of the resistor or what ever impedance you are using, not remove them.
|
|
#4
|
|||
|
|||
|
HRG systems are not permitted to serve line-to-neutral loads. So you should only have phase conductors and EGCs for any feeders and branch circuits supplied by a HRG system, and in particular there should be no _grounded_ circuit conductors (no neutrals).
-Jon |
|
#5
|
|||
|
|||
|
After rereading your OP, I am now under the impression that you are converting an existing 4-wire secondary into a 3-wire HRG. Yes, you are creating a system that is no longer solidly grounded.
Jon is correct, you must remove all existing L-N loads. Personally, I would 'safe off' any existing grounded conductors, so that they are not mistaken as being still in service.
__________________
I think I have already told you more than I know. |
|
#6
|
||||
|
||||
|
I agree with winnie, except you still need the grounded conductor ( neutral ) at the transformer ( X0 ) to connect to the HRG.
|
|
#7
|
|||
|
|||
|
Quote:
The HRG line load conductors are going to be installed where the main bonding jumper was. Rick
__________________
If I can't fix it, it's not broke. |
|
#8
|
|||
|
|||
|
Do the grounding impedance's have a line/load for lack of the proper terminoligy, or can
they be connected to either/or end. In other words can they be flipped 180deg and still work as they should. Thank You.
__________________
Frank Arizona,USA |
|
#9
|
|||
|
|||
|
Technically there is no reason for them to have any specific line-load, practically, however, most commercially available ones do. This is probably because of ancillary components like current sensors and pulsing contactors.
__________________
I think I have already told you more than I know. |
|
#10
|
|||
|
|||
|
Thanks Jim, By the way has anyone told you lately that you are a pretty good guy to
have hanging around this Forum ?
__________________
Frank Arizona,USA |
![]() |