Default High Resistance Ground

When installing a HRG to a 3-phase 4-wire wye transformer (existing transformer) would it be correct to say that the system is not a solidily grounded system, thereby requiring the existing grounded conductors be removed?

Rick
__________________
If I can't fix it, it's not broke.
  #2  
Old 11-04-2009, 04:48 PM
jim dungar jim dungar is offline
Moderator
 
Join Date: Feb 2003
Location: Wisconsin
Posts: 5,518
Default

Quote:
Originally Posted by RUWired View Post
When installing a HRG to a 3-phase 4-wire wye transformer (existing transformer) would it be correct to say that the system is not a solidily grounded system, thereby requiring the existing grounded conductors be removed?

Rick
You need to provide more details.

An HRG can supply a delta primary of a transformer.
The wye secondary is a separately derived system which can be solidly grounded and supply L-N loads, it does not impact the primary side HRG.
__________________
I think I have already told you more than I know.
  #3  
Old 11-04-2009, 05:03 PM
SG-1's Avatar
SG-1 SG-1 is offline
Senior Member
 
Join Date: Jul 2009
Location: South Carolina
Posts: 516
Default

You likely will need to move the grounded conductors to the correct side of the resistor or what ever impedance you are using, not remove them.
  #4  
Old 11-04-2009, 05:46 PM
winnie winnie is online now
Senior Member
 
Join Date: Apr 2006
Location: Portland, OR
Posts: 2,192
Default

HRG systems are not permitted to serve line-to-neutral loads. So you should only have phase conductors and EGCs for any feeders and branch circuits supplied by a HRG system, and in particular there should be no _grounded_ circuit conductors (no neutrals).

-Jon
  #5  
Old 11-04-2009, 06:19 PM
jim dungar jim dungar is offline
Moderator
 
Join Date: Feb 2003
Location: Wisconsin
Posts: 5,518
Default

After rereading your OP, I am now under the impression that you are converting an existing 4-wire secondary into a 3-wire HRG. Yes, you are creating a system that is no longer solidly grounded.

Jon is correct, you must remove all existing L-N loads. Personally, I would 'safe off' any existing grounded conductors, so that they are not mistaken as being still in service.
__________________
I think I have already told you more than I know.
  #6  
Old 11-04-2009, 06:34 PM
SG-1's Avatar
SG-1 SG-1 is offline
Senior Member
 
Join Date: Jul 2009
Location: South Carolina
Posts: 516
Default

I agree with winnie, except you still need the grounded conductor ( neutral ) at the transformer ( X0 ) to connect to the HRG.
  #7  
Old 11-04-2009, 07:51 PM
RUWired RUWired is offline
Senior Member
 
Join Date: Feb 2006
Location: Pa.
Posts: 1,780
Default

Quote:
Originally Posted by jim dungar View Post
After rereading your OP, I am now under the impression that you are converting an existing 4-wire secondary into a 3-wire HRG. Yes, you are creating a system that is no longer solidly grounded.

Jon is correct, you must remove all existing L-N loads. Personally, I would 'safe off' any existing grounded conductors, so that they are not mistaken as being still in service.
Thanks for all the replies. I am installing a HRG on the secondary of an existing 3-phase 4-wire wye secondary transformer with existing grounded conductors going out with each feeder. I need to identify all the single phase 277 volt loads on each feeder and deal with them. Most are lighting panels that will get a new 3-wire to 4-wire transformer. The existing grounded conductors with each feeder i will reidentify them as equipment grounding conductors and move them to the ground bar and reidentify the equipment as 3-wire.

The HRG line load conductors are going to be installed where the main bonding jumper was.

Rick
__________________
If I can't fix it, it's not broke.
  #8  
Old 11-05-2009, 10:10 PM
benaround benaround is offline
Senior Member
 
Join Date: Mar 2004
Location: Arizona
Posts: 3,909
Default

Do the grounding impedance's have a line/load for lack of the proper terminoligy, or can

they be connected to either/or end. In other words can they be flipped 180deg and still

work as they should. Thank You.
__________________
Frank Arizona,USA
  #9  
Old 11-05-2009, 11:27 PM
jim dungar jim dungar is offline
Moderator
 
Join Date: Feb 2003
Location: Wisconsin
Posts: 5,518
Default

Quote:
Originally Posted by benaround View Post
Do the grounding impedance's have a line/load for lack of the proper terminoligy, or can they be connected to either/or end. In other words can they be flipped 180deg and still work as they should. Thank You.
Technically there is no reason for them to have any specific line-load, practically, however, most commercially available ones do. This is probably because of ancillary components like current sensors and pulsing contactors.
__________________
I think I have already told you more than I know.
  #10  
Old 11-06-2009, 06:48 AM
benaround benaround is offline
Senior Member
 
Join Date: Mar 2004
Location: Arizona
Posts: 3,909
Default

Thanks Jim, By the way has anyone told you lately that you are a pretty good guy to

have hanging around this Forum ?
__________________
Frank Arizona,USA
Closed Thread

CEU Banner Forum Pages

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 12:50 PM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.