Default High Resistance Ground
When installing a HRG to a 3-phase 4-wire wye transformer (existing transformer) would it be correct to say that the system is not a solidily grounded system, thereby requiring the existing grounded conductors be removed?
Rick
__________________
If I can't fix it, it's not broke.
  #2
Old 11-04-2009, 05:48 PM
jim dungar jim dungar is offline
Default
Quote:
Rick
You need to provide more details.
An HRG can supply a delta primary of a transformer.
The wye secondary is a separately derived system which can be solidly grounded and supply L-N loads, it does not impact the primary side HRG.
__________________
I hope I said, what I meant to say, the way I meant it.
  #3
Old 11-04-2009, 06:03 PM
SG-1's Avatar
SG-1 SG-1 is offline
Default
You likely will need to move the grounded conductors to the correct side of the resistor or what ever impedance you are using, not remove them.
  #4
Old 11-04-2009, 06:46 PM
winnie winnie is offline
Default
HRG systems are not permitted to serve line-to-neutral loads. So you should only have phase conductors and EGCs for any feeders and branch circuits supplied by a HRG system, and in particular there should be no _grounded_ circuit conductors (no neutrals).
-Jon
  #5
Old 11-04-2009, 07:19 PM
Default
After rereading your OP, I am now under the impression that you are converting an existing 4-wire secondary into a 3-wire HRG. Yes, you are creating a system that is no longer solidly grounded.
Jon is correct, you must remove all existing L-N loads. Personally, I would 'safe off' any existing grounded conductors, so that they are not mistaken as being still in service.
__________________
  #6
Old 11-04-2009, 07:34 PM
SG-1's Avatar
Default
I agree with winnie, except you still need the grounded conductor ( neutral ) at the transformer ( X0 ) to connect to the HRG.
  #7
Old 11-04-2009, 08:51 PM
Default
Thanks for all the replies. I am installing a HRG on the secondary of an existing 3-phase 4-wire wye secondary transformer with existing grounded conductors going out with each feeder. I need to identify all the single phase 277 volt loads on each feeder and deal with them. Most are lighting panels that will get a new 3-wire to 4-wire transformer. The existing grounded conductors with each feeder i will reidentify them as equipment grounding conductors and move them to the ground bar and reidentify the equipment as 3-wire.
The HRG line load conductors are going to be installed where the main bonding jumper was.
Rick
__________________
  #8
Old 11-05-2009, 11:10 PM
benaround benaround is offline
Default
Do the grounding impedance's have a line/load for lack of the proper terminoligy, or can
they be connected to either/or end. In other words can they be flipped 180deg and still
work as they should. Thank You.
__________________
Frank Arizona,USA
It's what you learn after you know it all that counts !!
  #9
Old 11-06-2009, 12:27 AM
Default
Quote:
Originally Posted by benaround View Post
Do the grounding impedance's have a line/load for lack of the proper terminoligy, or can they be connected to either/or end. In other words can they be flipped 180deg and still work as they should. Thank You.
Technically there is no reason for them to have any specific line-load, practically, however, most commercially available ones do. This is probably because of ancillary components like current sensors and pulsing contactors.
__________________
  #10
Old 11-06-2009, 07:48 AM
Default
Thanks Jim, By the way has anyone told you lately that you are a pretty good guy to
have hanging around this Forum ?
__________________
Frank Arizona,USA
Reply
NEC Ready Forums
Search this Thread:
Advanced Search
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
- Archive - Top
Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.