Table 210.21(B)(3)

Status
Not open for further replies.

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
Would someone be so kind as to explain to me the logic of the 40 or 50 amp receptacle allowed to be used on a 40 amp circuit? Would attaching a 50 amp load to a 50 amp receptacle, trip the 40 amp breaker? I see in the table that such a condition is not allowed on the 15 amp circuit. Any explanation for this?
 