Quick question guys, i have a 208/120 feed to a step up transformer to 277/480. The 480 is needed for a elevator controler locator in a machine room 5 floors up. The print calls for a disconnect in the machine room near the controller room. Do i also need to put a disconnect near the transformer on the secondary side. The panel feeding the transformer is 15 ft away, do i need a disconnect on the primary or is the panel sufficient?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
As far as the primary, 450.14 accepts an "in sight from" disconnect.
As far as the secondary, see 240.21(C). With a 480/277 secondary, you will need to comply with the 240.21(C) secondary rules. Most commonly the 25ft rule is applicable.