Can al and copper conductors be used. For example. 1 hot copper and the second hot aluminum?


Sent from my LGLS770 using Tapatalk

Take a close look at 310.10(H), especially 310.10(H)(2).

It is not clear to me what you are actually asking so I do not have an answer for you.

If you are asking if you can make one phase paralleled Al and the other paralleled Cu, the answer is different than if you want to use an Al and Cu conductor in parallel on the same phase.
 

electricalist

Senior Member
Location
dallas tx
My buddy is studying for his masters and said he couldnt find where is says u cant have a phase paralleled 1 al and 1 al

Sent from my LGLS770 using Tapatalk
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
My buddy is studying for his masters and said he couldnt find where is says u cant have a phase paralleled 1 al and 1 al

Sent from my LGLS770 using Tapatalk
If both conductors of A phase are AL why would there be a problem?

Roger
 

Carultch

Senior Member
Location
Massachusetts
My buddy is studying for his masters and said he couldnt find where is says u cant have a phase paralleled 1 al and 1 al

Sent from my LGLS770 using Tapatalk

You can use a completely different configuration for all three phases, as long as your configuration OF EACH PHASE is internally identical.

Why you would want to do that, I do not know. It would be difficult in a practical sense of building a phase diverse feeder, and difficult to convince the inspector that it meets the NEC. Plus your voltage drop calculations are going to be confusing as hell.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Can 1 be al and 1 cu

Sent from my LGLS770 using Tapatalk

Petersonra's post has the code section, each phase has to be of the same characteristics but the different phases do not, for example, Phase A can be made up of AL XHHW and B could be CU THWN-2

Roger
 

electricalist

Senior Member
Location
dallas tx
Thanks actiondave. I misunderstood the question my buddy and i were debating. You answer what he was asking.

Sent from my LGLS770 using Tapatalk
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Thanks for all the replies.
Is there a instance where a being co and b being al would be used?

Sent from my LGLS770 using Tapatalk

It is not prohibited so it is strictly a design decision.

For instance, you might have some copper wire left over from an old job that you want to use up so you run one phase in copper and the rest in AL.

Or maybe you run one phase in copper because it lets you use a smaller conduit.
 