Phase Identification

Status
Not open for further replies.

LYLE2231

Member
I've looked in Art 215. A question put to me was "Is there anywhere in the code that dictates the ID of phases for feeds & sub-feeds?" The only place I can remember putting colored tape on phase conductors was from the spec's on a job. Comments requested. Best, Lyle:)
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Required if the premises has more than one voltage system per 210.5
 

cpal

Senior Member
Location
MA
215.12(C), 210.5(C), 517.160(A) (5).

215 and 210 require identification of the conductors by system and phase (08)

BUT they do not require color coding !!!!

517,160 ,110.15, and 230.56 do
 

jusme123

Senior Member
Location
NY
Occupation
JW
120/208v and 277/480v should be required to be color coded, the code should not be silent on this.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
120/208v and 277/480v should be required to be color coded, the code should not be silent on this.

Make a code proposal.:)

I have identified motor circuit conductors with T1,T2, and T3 before with wire markers and used all black wires. The conductors were identifed at all boxes and terminations.