After a long run of increased size conductor[increased to avoid voltage drop] is it nessecary to cotinue the incresed size to the device being wired or can the conductor size be decreased to the size that would normally be required for the last twenty five ft.?The conductors would be spliced in a j-box at or around 25 ft. before the device.It is a 30 amp 240 v single phase receptacle.The branch circuit feeders will be no. 6 thhn copper spliced to no. 10 thhn copper.Thanks GT.