Distance between electric handholes 24"X23 1/2"X12" Deep

Status
Not open for further replies.

eeeee

Member
Location
Alaska
I have some 2000 ft runs for some area lights mounted on 35' poles. I have some electric concrete handholes selected that are 24"X23 1/2"X12" deep. Cable size is #10AWG cable. Spool size from manufacturer is 1000'. How oftend should I place the hanholes, every 500'??
 

480sparky

Senior Member
Location
Iowegia
With a limit of 1000' of cable, and a 2000' run, I'd say you need to put them halfway between the power source and the pole.
 

K2500

Senior Member
Location
Texas
Depending on burial depth, and weather or not you rounded up or down to 2000', half way may have you coming up short.
 
Status
Not open for further replies.
Top