We had an inspector here in Siskiyou County,CA. that told us that we didn't need to ground or put a separate disconnect to a detached garage or out building so long as we had less than two circuits and it could be disconnected by as single lever(breaker). This guy was by the book! Now we have a new inspector that can't find this in the book and won't allow it. Do you know where it is? Because we can't find it either.
 

iwire

Moderator
Staff member
Location
Massachusetts
I assume you mean ground rods? If so see the exception to 250.32

As far as disconnecting means see 225.36 and its exception.
 