kelkmac
New member
- South Carolina
I guess we are both assuming its the main panel....but I guess assuming is not good...but it's a high probability.. (but is always why it sucks to comment on images with less than complete details provided...lol)If it is a sub panel the bond from netural to ground should only be in first panel, that is a netural to ground connection there.
The top of the photo cuts off the details of the buss bar / terminal bar electrical connections, but, with what is there, it appears that the top of both terminal bars are BOLTED to the same buss bar.conductors are not trimmed and making contact with second bar -- reason for concern? or just sloppy? Thx
AHHH...well in that logic I don't think it is THAT sloppy in order to assume the same as you have. Again one mans SLOP is another mans GLORY!My only reason for concern is that if it's sloppy in the panel, what else is sloppy? That kind of work might not be a big deal on a grounding bar, but on the back of a receptacle? Maybe they just sort of wrapped stranded wire around the screw and tightened. Makes me suspicious.
it is assumed that it is not....but the image is cut off at the top so it does appear that the bars are connected at the top.....but again eyes fail me.....So the assumption (unless the original OP says otherwise) that they are connected together in service equipment.so this is not a sub-panel ??
I don't see anything to be concerned about.
If people would just stop using those goofy Square D panels this wouldn't even be an issue.
I don't see anything wrong. I don't see anything that looks terribly messy.
... PetrosA, I prefer SQ D QO or Cutler Hammer tan handle. The panel that I hate is GE with skinny breakers.
