where would the definition of residential kitchen be wondering if a kitchenette (no cooking appliances) is required to have 2 - 20 amp circuits
 

480sparky

Senior Member
Location
Iowegia
Kitchen. An area with a sink and permanent facilities for food preparation and cooking. New to the 2008 NEC.
 
Last edited:

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
normbac said:
where would the definition of residential kitchen be wondering if a kitchenette (no cooking appliances) is required to have 2 - 20 amp circuits
Sounds like what we would call a breakfast room.

210.52(B) Small Appliances.
(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
 

480sparky

Senior Member
Location
Iowegia
normbac said:
So would it have to have cooking appliances that are permanent

That's my take on it.

This.....

Master_Bedroom.jpg


...IMPO is not a kitchen.
 

480sparky

Senior Member
Location
Iowegia
chris kennedy said:
Is that your work? I like the receptacles every 3 to 4 feet.

One is a phone, another is a Central Vac....

normbac said:
This is a good example at what state does it become a kitchen

There's no permanent facilities for cooking, so I say it's not a kitchen.
 

benaround

Senior Member
Location
Arizona
480sparky said:
Unless you are wiring to the '08, then you don't have a definition yet....

That looks like a kitchen to me.

It really looks like the definition of a commercial kitchen. 210.8(B)(2). 2005

If I had nothing to refer to ( like plans or EI ) I would wire it like a 2008

kitchen or like a similar location 2005. I think that is what norm is asking.
 

normbac

Senior Member
benaround said:
That looks like a kitchen to me.

It really looks like the definition of a commercial kitchen. 210.8(B)(2). 2005

If I had nothing to refer to ( like plans or EI ) I would wire it like a 2008

kitchen or like a similar location 2005. I think that is what norm is asking.
Actually I was just curious because I have to wire a similiar kit in a pool house it has two outlets and I dont see the need for 2-20 amp recepts
 

wirebender

Senior Member
benaround said:
That looks like a kitchen to me.

It really looks like the definition of a commercial kitchen. 210.8(B)(2). 2005

If I had nothing to refer to ( like plans or EI ) I would wire it like a 2008

kitchen or like a similar location 2005. I think that is what norm is asking.


Where are the permanent facilities for cooking?
 

C3PO

Senior Member
Location
Tennessee
stickboy1375 said:
It does? How so? Looks like a countertop with a sink to me.

I agree. If the microwave was built into the cabinet then it would be, but in 480's picture that is not a kitchen.
 

SEO

Senior Member
Location
Michigan
C3PO said:
I agree. If the microwave was built into the cabinet then it would be, but in 480's picture that is not a kitchen.
What if it had an electric stove that was cord connected and not built in?
 

C3PO

Senior Member
Location
Tennessee
DanZ said:
If the microwave has it's own circuit, what's the difference between a microwave as a permanent means of cooking, and an electric range?

I could see this one going both ways, depending on the AHJ, I think.

A microwave sitting on the counter is not permanent. If it was a microwave/hood or something like built into the cabinets then it would be considered permanent IMPO.
 