    This is more a ?
    I would like to ask
    I have a new home " " now this home has 3 bedrooms ,2 bathrooms 1 kitchen and so on.
    2 bedrooms have a 12/3 as a line (to different circuits sharing the same neutral) (phase "a"=n of out lets --- phase "b"=n of out lets ) (phase "a" bedroom1--- phase "b" bedroom2)
    Now the question is: Can we install on the circuit panel a AFCI type of breakers for this 2 particular branch circuits?
  2. #2
    Join Date
    Oct 2006
    Baltimore, MD
    Posts
    3,161
    Quote Originally Posted by bb_becker
    This is more a ?
    I would like to ask
    You will not be able to use single pole AFCIs. They require separate grounded conductors. You will have to use a 2 pole AFCI. I don't think all manufacturers make them.
    John from Baltimore "One Day at a Time"
  3. #3
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    I would use a single pole AFCI for each 12/3 and jump the red and black together to the same breaker.
    No reason a single 20 amp circuit can not supply the lights and receptacles in a bedroom.
  4. #4
    Join Date
    May 2008
    Northern Il
    Posts
    92
    Quote Originally Posted by JohnJ0906
    John,
    2-pole arc fault breakers?? Who manufactures those?? I have yet to see them. Also, i would think that you would have the same issue that you would using a MWBC that is GFCI protected. Shared neutral can cause nuisance tripping. I would also appreciate an explanation of how you can have a "2 pole AFCI with "separate" "grounded" conductors, which would indicate TWO circuits, not a MWBC. The "grounded" conductor would be your neutral.....
  5. #5
    Join Date
    Feb 2003
    Minnesota
    Posts
    6,774
    Quote Originally Posted by SPARKS40
    In the branch feeder, Cutler Hammer, Siemens & GE. The combination AFCI is available in single pole, only, at present.
    The question to bb_becker is whether that jurisdiction requires combination or branch feeder AFCI.
    When the two neutrals are wirenutted together and a pigtail is connected from the wirenut to the neutral load terminal of a two pole AFCI (or GFCI), the pigtail is a "shared neutral" making the whole setup a multiwire branch circuit.
    Another Al in Minnesota
  6. #6
    Join Date
    Jun 2007
    Ogdensburg, NY
    Posts
    2,257
    Arrow
    Quote Originally Posted by iwire
    Notice Bob said "jump" to the breaker. Most breakers are rated for one conductor only and not double tapped.
    Old and in the Way.......
  7. #7
    Join Date
    Oct 2006
    Litchfield, CT
    Posts
    8,699
    Quote Originally Posted by 76nemo
    Dont worry, the Home Inspectors always find that violation.