RTD in class 1 div 2 area.....

Status
Not open for further replies.

connelyd

Member
Location
Columbus, MS
I currently have RTDs installed in a class 1 div 2, group B location(on top of an electrolytic tank in a thermowell) but the 4-20mA transmitters are installed in an unclassified area. The RTDs are connected via wirenuts in general purpose enclosures to more wire that then goes to the transmitters. All of the conduit used to run the wire is class 1 div 2 compliant. Is this an exceptable installation? I can't find anything in the code that would suggest it is not, but being young, I figured I should ask. Thanks in advance.

photo 2.jpg photo 3.jpg
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I currently have RTDs installed in a class 1 div 2, group B location(on top of an electrolytic tank in a thermowell) but the 4-20mA transmitters are installed in an unclassified area. The RTDs are connected via wirenuts in general purpose enclosures to more wire that then goes to the transmitters. All of the conduit used to run the wire is class 1 div 2 compliant. Is this an exceptable installation? I can't find anything in the code that would suggest it is not, but being young, I figured I should ask. Thanks in advance.

View attachment 8057 View attachment 8058

I don't think the wire nuts matter.

Take a look at 501.105 (B)
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
I currently have RTDs installed in a class 1 div 2, group B location(on top of an electrolytic tank in a thermowell) but the 4-20mA transmitters are installed in an unclassified area. The RTDs are connected via wirenuts in general purpose enclosures to more wire that then goes to the transmitters. All of the conduit used to run the wire is class 1 div 2 compliant. Is this an exceptable installation? I can't find anything in the code that would suggest it is not, but being young, I figured I should ask. Thanks in advance.
...
Assuming, "... All of the conduit used to run the wire is class 1 div 2 compliant..." is correct, what about the cable? Again assuming the cable is compliant with 501.10(B)(4),(5), or (6) AND 501.30(B) Exception, the installation appears acceptable.

The wirenuts are acceptable.
 