fillmorr

Member
Location
Mansfield Ohio
Has anyone had trouble with those switches that light up when off? I havent investigated or replaced it yet but one night i hit the wall and turned the light on and the other night was givin a shock from it
 

hurk27

Senior Member
Switches that light up when the load is off are generally put in series with the load (across the contact) and don't need to use a neutral or ground as a return path, so if this is the type of switch then its sounds like a problem with the switch having an internal connection problem and the strap is not grounded.
 

kwired

Electron manager
Location
NE Nebraska
Was the shock a definite AC current shock or just static discharge when you touched it?

Just hitting the wall should not cause operation of a good condition switch, maybe something is defective or broken with it.
 

fillmorr

Member
Location
Mansfield Ohio
It was a shock there was a spark with it and tingling fingers. I plan to replace. Its in a moble home and the wiring has been a headace since moving in and been working to replace most devices and switch everything from the back stab connects to the screw termanils
 